yesterday I replaced the battery of my Smart-UPS750.
I thought this would be the right time for updated the firmware of the Network Managment Card 2.
So I have done it.
After that I would run the runtime calibration which was refused by NMC every time.
I found a post in the forum, that the firmware from the UPS has should be updated too. So I did it and I updated the UPS from 5 (ID17) to 7.1 (ID17).
Unfortunately the calibration does not work after all.
The following have I done also:
  • discharging and charging the battery
  • restoring to factory defaults
  • reboot of NMC and UPS.
But nothing solved the problem.
Has anyone any further suggestion how to solve the problem?
Thank you.
Best Regards,
Martin
  • calibration
  • network-management-card
  • problem
  • smart-ups
Posted: ‎2021-06-28 02:22 AM . Last Modified: ‎2024-03-18 11:21 PM
20568
Hi Bill,
this was the right hint. Thank you.
I tryed to start the calibration from front panel, which was refused too.
But here I got a helpfull error message. "Calibration need at at least 10% load".
So I put more consumer to the outlets, and now I could start the calibration from NMC.
Sorry for the inconvenience.
Best Regards,
Martin
Replies 8
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander
Normally the only reason for the UPS to refuse the calibration command is a) the battery is not at 100% or b) it is doing something with the battery already (on battery, self-test, etc.).
I'd suggest running a self-test, and if that passes, try the calibration again once the battery returns to 100% from the self-test.
Hi Terry,
thank you for your answer.
I have done this before.
The self test has passed before and I have waited until the battery load was 100.0%.
Today I tried the calibration and it was refused too, after passed self test (yesterday). (As you can see on se5.png)
Terry_Kennedy_apc
Commander
I think you'll need to wait for the APC folks to see this, then. Here in the US, Monday is a holiday. You can find your local support contact info here.
Can you run the calibration test from the Smart-UPS LCD panel? To do this you click on the Esc key, use the up or down arrow to scroll to Test & Diags, click on the enter key, use the up or down arrow to scroll to Calibration Test.
20569
Hi Bill,
Best Regards,
Martin
Binod
Binod
Cadet
Posted: ‎2022-03-01 02:41 PM
In response to BillP
19774
Hi ,
In my case self-test passed but still the callibration got the result: Refused..
Cause: load too low
Model: Smart-UPS 750
Firmware: UPS 08.3
Manufature date: 2013
Any idea ?
Binod
TonKei
Lieutenant TonKei Lieutenant
Lieutenant
Posted: ‎2022-03-01 11:02 PM
In response to Binod
Hello Binod
There is a FAQ document detailing the requirements for doing a runtime calibration on the SMT/SMX units.
You can find the FAQ here -> https://www.apc.com/us/en/faqs/FA314748/
In short, there are minimum requirements that need to be met, or the unit will refuse the calibration.
"UPS load greater than a minimum threshold, which is proportional to the number of External Battery Packs (XBP) connected. With no XBP connected, the minimum required load is 10% (SMX or SMT); with one XBP: 25%; with 2 XBPs: 40%; with 5 or more XBPs: 85%"
On another note, you are posting to a thread that was marked as solved a while back, which makes your post very easy to overlook.
Best regards
Tonny
Oleg8R
Oleg8R
Cadet
Posted: ‎2024-10-23 04:17 PM
Have same issue. Calibration refused with a note "state of charge not acceptable". UPS load is higher than 10% and battery is fully charged.
Model
Smart-UPS 1500
SKU
SMT1500RMI2U
Serial Number
3S2238X10394
Firmware Revision
UPS 09.3 (ID18)
Manufacture Date
09/20/2022
Apparent Power Rating
1500 VA
Real Power Rating
1000 W
Battery SKU