how to reset APDU10350ME power meter

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • how to reset APDU10350ME power meter
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
xcanehan
Crewman xcanehan
Crewman

Posted: ‎2024-10-21 07:49 AM

0 Likes
7
1734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-21 07:49 AM

how to reset APDU10350ME power meter

Hi, 

How can I reset the power meter of a APDU10350ME (firmware version 2.0.6.3) ?
I did not find this via CLI our through web login. Documentation does not mention this.

 

Thanks,

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-23 04:28 AM

In response to xcanehan
1 Like
0
1651
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 04:28 AM

It’s been a long time since working on this specific PDU. But verify the menu is set to advanced vs basic.

 
There should be a tab to reset the energy consumption. Worst case you need to follow the steps outlined in the manual I highlighted.

 

The setup wizard should also bring you to a default state. Don’t recall if that erases the power metrics though.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

xcanehan
Crewman xcanehan
Crewman

Posted: ‎2024-10-24 12:31 AM

0 Likes
1
1607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 12:31 AM

This lead me to the solution. 

In Control and Manage tab, right hand side, there is a Reset PDU Energy action:

xcanehan_0-1729754645661.png

I missed it during previous explorations. This action is not described in the current Advanced User Guide (09/2023).

I still have to find a way to programmatically reset it, I hope via snmp.

This will ease our commission procedure for new IT hardware. Many thanks.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Teken
Kirk Teken
Kirk

Posted: ‎2024-10-22 05:46 AM

0 Likes
1
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 05:46 AM

Please review the full users manual on page 33 & 65. Which outlines how to default the unit to a factory state:

 

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=NetShelter+Rack+PDU...

Reply

Link copied. Please paste this link to share this article on your social media post.

xcanehan
Crewman xcanehan
Crewman

Posted: ‎2024-10-22 09:05 AM

In response to Teken
0 Likes
0
1666
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-22 09:05 AM

Thank you for your suggestion.

However, I would like to avoid nuking all configuration.
I should have been clearer: can I just reset the energy meter, which states how many kilowatts have been used since (first start of PDU)?

Clearing all data logs (page 28 of said documentation) does not reset the energy meter.

Reply

Link copied. Please paste this link to share this article on your social media post.

PrzemekSz
Ensign PrzemekSz Ensign
Ensign

Posted: ‎2024-10-23 12:25 AM

1 Like
0
1668
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 12:25 AM

Hi,

If your goal is to check energy consumption on specific period of time without default rPDU to factory state you may use Data Center Expert or IT Expert. You can easily check delta value of each sensor on specific period of time, which means also consumption on specific period of time.
Both can be tested for free. IT Expert:
https://ecostruxureit.com/298771/

ITE report.PNG

 

DCE:

https://www.apc.com/us/en/product/AP94VMTRL/software-ecostruxure-it-data-center-expert-virtual-appli... 

DCE report.PNG

Reply

Link copied. Please paste this link to share this article on your social media post.

xcanehan
Crewman xcanehan
Crewman

Posted: ‎2024-10-23 04:10 AM

0 Likes
1
1664
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 04:10 AM

Thank you,

 

I'll wait a bit for a basic solution at the PDU level, but this is the closest to my need.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-23 04:28 AM

In response to xcanehan
1 Like
0
1652
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-23 04:28 AM

It’s been a long time since working on this specific PDU. But verify the menu is set to advanced vs basic.

 
There should be a tab to reset the energy consumption. Worst case you need to follow the steps outlined in the manual I highlighted.

 

The setup wizard should also bring you to a default state. Don’t recall if that erases the power metrics though.

Reply

Link copied. Please paste this link to share this article on your social media post.

xcanehan
Crewman xcanehan
Crewman

Posted: ‎2024-10-24 12:31 AM

0 Likes
1
1608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 12:31 AM

This lead me to the solution. 

In Control and Manage tab, right hand side, there is a Reset PDU Energy action:

xcanehan_0-1729754645661.png

I missed it during previous explorations. This action is not described in the current Advanced User Guide (09/2023).

I still have to find a way to programmatically reset it, I hope via snmp.

This will ease our commission procedure for new IT hardware. Many thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-10-24 01:31 AM

In response to xcanehan
0 Likes
0
1605
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-24 01:31 AM

If one of my replies provided the solution please do mark it as so.

 

So that information can help the next person asking the same. 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore