Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Run SU5000RMT5U on 240v?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Run SU5000RMT5U on 240v?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
12
1313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Run SU5000RMT5U on 240v?

Hey everyone. πŸ™‚

My company has inherited an older (circa 2003) but working SmartUps 5000. The original location had it running on 208v, which is what the nominal voltage is for that UPS. However, the location where we'd like to use it has 120 and 240v only.

According to the specifications: (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU5000RMT5U)

  • Input voltage range for main operations: 157 - 255V
  • Input voltage adjustable range for mains operation: 151 - 268V

This suggests that it can run at 240v just fine. However, the PDF version of the manual (available on the APC site) only states 208v in the specifications and does not mention what needs to be changed/altered in order for the UPS to function properly on 240v.

So, my two questions are:

  • Can this UPS function properly on 240v?
  • If so, what needs to be changed on the UPS in order to run on 240v?

Thanks in advance! πŸ™‚

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Hello,

Any of the Smart UPS models beginning with "SU" or "SUA" with a "T" in their part number at the end are designed for nominal 208V only. You're going to have multiple problems feeding it 240V including:

  • The highest transfer point (where it will go to battery) will be 239V.
  • The range you see in the PDFs and web page for input voltage are accounting for Automatic Voltage Regulation (AVR) functions.
  • Even if you set the transfer point to 239V, the UPS won't run well and will be transferring constantly to and from AVR and on battery operation.
  • The UPS will not run well/reliably and you risk the UPS not operating online (as I noted) and also when it won't turn on
  • The 120V convenience outlets (limited to 400VA) will output a little bit higher voltage than 120V.
  • We have units specifically designed for 208V or 240V which allow you to change between them (like Smart UPS RT) and this UPS does not have that option unfortunately.

I don't think there is anything you can change to get this to operate on 240V, not that we could recommend or support anyway.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Hey everyone. πŸ™‚

My company has inherited an older (circa 2003) but working SmartUps 5000. The original location had it running on 208v, which is what the nominal voltage is for that UPS. However, the location where we'd like to use it has 120 and 240v only.

According to the specifications: (http://www.apc.com/resource/include/techspec_index.cfm?base_sku=SU5000RMT5U)

  • Input voltage range for main operations: 157 - 255V
  • Input voltage adjustable range for mains operation: 151 - 268V

This suggests that it can run at 240v just fine. However, the PDF version of the manual (available on the APC site) only states 208v in the specifications and does not mention what needs to be changed/altered in order for the UPS to function properly on 240v.

So, my two questions are:

  • Can this UPS function properly on 240v?
  • If so, what needs to be changed on the UPS in order to run on 240v?

Thanks in advance! πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Hello,

Any of the Smart UPS models beginning with "SU" or "SUA" with a "T" in their part number at the end are designed for nominal 208V only. You're going to have multiple problems feeding it 240V including:

  • The highest transfer point (where it will go to battery) will be 239V.
  • The range you see in the PDFs and web page for input voltage are accounting for Automatic Voltage Regulation (AVR) functions.
  • Even if you set the transfer point to 239V, the UPS won't run well and will be transferring constantly to and from AVR and on battery operation.
  • The UPS will not run well/reliably and you risk the UPS not operating online (as I noted) and also when it won't turn on
  • The 120V convenience outlets (limited to 400VA) will output a little bit higher voltage than 120V.
  • We have units specifically designed for 208V or 240V which allow you to change between them (like Smart UPS RT) and this UPS does not have that option unfortunately.

I don't think there is anything you can change to get this to operate on 240V, not that we could recommend or support anyway.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

No problem! Please let us know if you have further questions. laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Hi Angela,

Thanks for clarifying input voltage for that specific UPS model.

Would you know which Smart-UPS 5000VA-rated model could be acceptable for 240V input ? The only other one I can see on APC's site is this one:

SUA5000R5TXFMR

Thanks for confirming this, it will greatly help.

Regards,

Alexandre

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Hi Alexandre,

I was looking at APC Product Information for Uninterruptible Power Supply (UPS) <meta http-equiv="Content-Type" /> - ...

Other considerations would be the Symmetra 6K Rack Mount or Symmetra LX 8kVA (which could cover 5kVA as well but they do 208V/240V).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Hi Angela,

I clicked on the link you provided, but I cannot find anything resembling "SURTD"... I even did a search on the APC website.

Could you provide me with an exact model number and/or link?

And would be able to confirm if the model SUA5000R5TXFMR is suitable for 240V input?

Thanks,

Alexandre

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:14 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Oops, I just saw that the SURTD models are online UPS... They are a bit out of my range, which is why the line-interactive SUA5000R5TXFMR model is interesting for me.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:12 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:12 AM

Ah I see. Sorry - I double checked and anything that is SUA5000 (so any variant of that SKU is 208V input only - the highest you can set the transfer point is 239V and it just won't run properly.

I also checked to verify what I thought - only those SURT models are 208/240V and then the other items I mentioned. Is there a way you can change this input at the location if an online UPS is not an option?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

Thanks Angela. Unfortunately, I cannot change the utility output to 208V at my location... frown I'm looking at the used market because this is for a college project where I teach, so maybe I should go for smaller models (3000VA), line-interactive, that can work at 240V input (or even 120V), and provide with 120V outputs. Double-conversion, online models are not affordable for us right now.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

Bummer. Wish we could find something.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

If I want to stay in the entry-level, line-interactive models, with 3000VA+, it looks like the 120V 3000VA Smart-UPS would be best suited to fit our utility (SMT3000RM2U). Otherwise, 230V, line-interactive models don't output 208V or 120V if I'm correct.

Unless I go with online models of course, per your recommendation.

I'll try to find a used SMT3000RM2U or SUA3000RM2U.

Thanks for everything Angela.

Alexandre

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

0 Likes
0
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-29 08:15 AM . Last Modified: β€Ž2024-03-12 03:11 AM

Hi Alexandre,

You're welcome. Are you able to split the (2) legs that make your 240V and that is how you're able to use 120V instead?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of