Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
High Earth voltage at Smart UPS Output on battery operation
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:15 AM. Last Modified: 2024-03-1203:11 AM
High Earth voltage at Smart UPS Output on battery operation
I understand after reading APC support (FAQ FA156549) but is it possibel to to reduce the output Earth voltage(Between Netral to Earth) for client satisfaction after doing some hardware changes with Earth, Netral or Using separate Earth or some component network?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:15 AM. Last Modified: 2024-03-1203:11 AM
While "On Battery," safety agencies (UL, VDE, etc.) require the UPS input connections to be disconnected from the utility input to prevent "backfeed" power/voltage from the UPS batteries being applied to the UPS input terminals. Because the Neutral must also include this "backfeed" protection (we do it by opening a relay), the output Neutral to Ground voltage will "float" to approx half the voltage between output Line & Neutral. For a 230Vac system, the N-GND voltage can be 115Vac. This does not become a safety hazard because the output L & N conductors are not user-accessible. They are both always considered "high voltage" conductors.
If the UPS output must have a N-GND connection for zero volts while the UPS is "On Battery," an output isolation transformer must be attached to the UPS output so that a new N-GND connection can be made without creating a ground loop. We sell isolation transformers that can be used for this, if required.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2908:15 AM. Last Modified: 2024-03-1203:11 AM
While "On Battery," safety agencies (UL, VDE, etc.) require the UPS input connections to be disconnected from the utility input to prevent "backfeed" power/voltage from the UPS batteries being applied to the UPS input terminals. Because the Neutral must also include this "backfeed" protection (we do it by opening a relay), the output Neutral to Ground voltage will "float" to approx half the voltage between output Line & Neutral. For a 230Vac system, the N-GND voltage can be 115Vac. This does not become a safety hazard because the output L & N conductors are not user-accessible. They are both always considered "high voltage" conductors.
If the UPS output must have a N-GND connection for zero volts while the UPS is "On Battery," an output isolation transformer must be attached to the UPS output so that a new N-GND connection can be made without creating a ground loop. We sell isolation transformers that can be used for this, if required.