Restarting Servers when power is restored

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Restarting Servers when power is restored
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
3
4746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

Restarting Servers when power is restored

"They are also set to then send a startup command to the servers once the UPS has been back on power for a certain time and has enough battery power to handle the whole load for enough time that they could shut down again if needed"

How would I go about configuring this? Is this something I would setup on our NMC? This response was posted by an anonymous source online. 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • communication
  • network-management-card
  • PowerChute
  • startup
  • windows
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
0
4746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

Hi,

For the servers to restart following a shutdown event you must configure the BIOS of the servers to restart when AC is restored. Since the servers are off there is no way for an application to command them on. To ensure that AC is cut to allow the server to power back up after a power failure you need to configure PowerChute Network Shutdown to shutdown the UPS. By doing so AC will be cut to the servers and when the BIOS see that AC has been restored the server will restart automatically. 

There is Knowledge Base document FA159550 on this subject and there have been quite a few discussions on this forum concerning this. The Knowledge Base document recommends setting the BIOS to last state however some people have recommend setting the BIOS to always on. I recommend setting the system to last state and if that is not compatible change to always on.

To configure a outlet group shutdown and power in the NMC go to Configuration - Outlet Groups (review the help files for assistance with the settings).  

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
0
4746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

Sam,

What model UPS are you asking about? Also, what is the model of the NMC and firmware? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
0
4746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

About UPS
 
Model: Smart-UPS SRT 3000
SKU: SRT3000RMXLT
Serial Number: AS1624390199
Firmware Revision: UPS 05.3 (ID1010)
Manufacture Date: 06/15/2016
 
Apparent Power Rating: 3000 VA
Real Power Rating: 2700 W
 
Battery SKU: APCRBC152
 
   
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

0 Likes
0
4747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:56 AM . Last Modified: ‎2024-03-13 01:11 AM

Hi,

For the servers to restart following a shutdown event you must configure the BIOS of the servers to restart when AC is restored. Since the servers are off there is no way for an application to command them on. To ensure that AC is cut to allow the server to power back up after a power failure you need to configure PowerChute Network Shutdown to shutdown the UPS. By doing so AC will be cut to the servers and when the BIOS see that AC has been restored the server will restart automatically. 

There is Knowledge Base document FA159550 on this subject and there have been quite a few discussions on this forum concerning this. The Knowledge Base document recommends setting the BIOS to last state however some people have recommend setting the BIOS to always on. I recommend setting the system to last state and if that is not compatible change to always on.

To configure a outlet group shutdown and power in the NMC go to Configuration - Outlet Groups (review the help files for assistance with the settings).  

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore