APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
Hi, I have a two to three week old SMT3000 manufactured in July 2012 that I think may have battery problems. I initiated a run-time calibration test for the first time today and the battery remaining percentage dropped to 66% within two to three seconds of initiating the test. I don't think this is correct and can anyone else tell me what I can do to confirm that the RBC55 that is installed is good or not? The load percentage at the time was right around 20% when the test was initiated. Thanks in advance!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
Well we don't recommend doing runtime cals unless there is a specific reason such as low runtime etc. We also recommend have at least a 30 % load when doing a calibration. What is your current load and runtime via the display? Also, is the battery capacity at 100 %?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
Well we don't recommend doing runtime cals unless there is a specific reason such as low runtime etc. We also recommend have at least a 30 % load when doing a calibration. What is your current load and runtime via the display? Also, is the battery capacity at 100 %?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
Hi and thanks. The load I currently have is about 20% and the runtime was about 25 minutes at that load before the runtime calibration routine self-termindated.