Hi everyone,
Last night i had situation regarding Powerchute client, my UPS model is Smart-UPS 5000 and what happened is the UPS goes to on battery mode and after 10 minutes the server shutdown although the Low battery duration was set to 30 minutes and maximum required delay was set to 20 minutes whatever the next was more strange for me the server restored power after the electricity come back again then after 5 minutes the server powered off again by Powerchute signal, i don't know what is going on and my situation is critical because we had an electricity issues everyday in the site so your support will be appreciated.
UPS Network Management Card 2
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-13 01:12 AM
Your screenshot shows low battery duration is 15 minutes, not 30. You've probably adjusted it, but we'll use assume 15 minute.
If the low battery duration is 15 minutes, and PCNS hasn't been configured to shut down before low battery, and the UPS started a shutdown after 10 minutes, that implies your runtime was 25 minutes (15 minute low battery + 10 minutes before hitting low battery).
Once the UPS has been commanded to turn off which should happen when a server shuts down, it must turn off, even if power returns. This is to allow the servers to turn back on. That might be what you're seeing when the servers turn off 5 minutes after power returned. In that scenerio, the servers shut down and tell the UPS to turn off, power comes back, someone or something turns the servers back on before the UPS completes its shutdown cycle, then 5 minutes later the UPS turns off the output and turns it back on.
I'm not sure which UPS you have. If your UPS has outlet groups, you might want to look at the settings of the outlet groups for the turn off and turn on delays.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-13 01:12 AM
Your screenshot shows low battery duration is 15 minutes, not 30. You've probably adjusted it, but we'll use assume 15 minute.
If the low battery duration is 15 minutes, and PCNS hasn't been configured to shut down before low battery, and the UPS started a shutdown after 10 minutes, that implies your runtime was 25 minutes (15 minute low battery + 10 minutes before hitting low battery).
Once the UPS has been commanded to turn off which should happen when a server shuts down, it must turn off, even if power returns. This is to allow the servers to turn back on. That might be what you're seeing when the servers turn off 5 minutes after power returned. In that scenerio, the servers shut down and tell the UPS to turn off, power comes back, someone or something turns the servers back on before the UPS completes its shutdown cycle, then 5 minutes later the UPS turns off the output and turns it back on.
I'm not sure which UPS you have. If your UPS has outlet groups, you might want to look at the settings of the outlet groups for the turn off and turn on delays.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-13 01:12 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-13 01:12 AM
Thanks for your reply
UPS Model: Smart-UPS SRT 5000
NMC: AP9537SUM
let's say i want to deploy this scenario so what is the basic configuration for NMC and PSCN side.
- I want the UPS to send shutdown command to the server when the trigger of low Battery Duration will be 15 minutes and give three extra minutes to the server to gracefully shutdown before UPS shutdown outlet group and if the power back again UPS will wait 5 minutes before send to restore server power and what is the best scenario to apply outlet group for the turn off and turn on delays.
how to set the below parameter regarding the scenario that i want to deploy
- Low battery duration
- Maximum Required Delay
- Basic Low Battery Duration
- Shutdown Delay
- return Delay
- PowerChute shutdown parameters
- ups on battery event (PCNS)
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:55 AM . Last Modified: 2024-03-13 01:11 AM
Hi,
You need to set the Low Battery Duration to 15 minutes. Once the UPS fails below 15 minutes of available run-time it will signal PCNS and the OS will be commanded down. In PCNS configure either UPS power off or outlet group power off so when PCNS commands the OS down it will command the UPS or outlet group off. If you want all outlet groups to power off you must select UPS power off.
In the NMC go to Configure - Outlet Groups and configure Power off Delay for each of the outlet groups you want powered down. Set the Power off Delay to 3 minutes so after receiving the power down command from PCNS the outlet group/s will wait 3 minutes then cut power. Also in the Outlet Group configuration set the Reboot Duration to 300 seconds so that if AC during the Power off Delay the Outlet Group will wait for the Power off Delay to complete and the wait 5 minutes before restoring AC.
An explanation of each of NMC settings can be found in the NMC help files and PCNS also offers help files.
Use these settings to automatically shut down an outlet in response to one or more conditions. To enable a condition, mark its checkbox and configure its value; you can enable multiple conditions.
If you use PowerChute Network Shutdown (PCNS) on this outlet, be sure "Skip outlet off delay" is not checked so that PCNS clients can safely shutdown. Also, each PCNS client has its own set of conditions that may be configured to start a shutdown.