Hello,
I just setup a stand alone SMT750i today which is connected to a HP server via a USB Cable. The APC Software was installed and configured successfully. The server runs for about 30 mins and then shuts down gracefully.
One thing i noticed though was that when the server turned back on and I logged in, Windows asked me for a reason as to why the server turned off. Generally these details are specified before you click the shutdown and a description can be added.
But since it prompted me at logon it either,
a) didn't shutdown properly
b) when apc initiates the shutdown it doesn't fill in that information.
I am thinking it is the latter as the server did gracefully shutdown before the outlet groups turned off.
Is this correct?
Cheers
Peter Sheridan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
the answer is B per what you mentioned in your post. PCBE cannot fill in that field but has an event log of its own for review that you'd need to rely on.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
Great. Thanks Angela
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:56 AM . Last Modified: 2024-03-13 01:11 AM
the answer is B per what you mentioned in your post. PCBE cannot fill in that field but has an event log of its own for review that you'd need to rely on.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.