Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-30 08:07 PM . Last Modified: 2024-03-07 12:34 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:07 PM . Last Modified: 2024-03-07 12:34 AM
We have a Powerchute 3000xl, along with a network management card and each server has the Powerchute Network Shutdown installed. We had a power outage last night, and the APC did a graceful shutdown of all the servers, which is awesome, but it only brought one back online once the power was restored.
I checked the settings of the server that was brought back online automatically and it was no different from the rest of the servers. Any idea what settings I should be looking at if I want the servers to come back online once power has been resotored?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:07 PM . Last Modified: 2024-03-07 12:34 AM
this behavior should not have anything to do with the UPS or the NMC, it depends on the BIOS settings.
check out these knowledgebase articles -> http://nam-en.apc.com/app/answers/detail/a_id/1003 , http://nam-en.apc.com/app/answers/detail/a_id/948/
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:07 PM . Last Modified: 2024-03-07 12:34 AM
this behavior should not have anything to do with the UPS or the NMC, it depends on the BIOS settings.
check out these knowledgebase articles -> http://nam-en.apc.com/app/answers/detail/a_id/1003 , http://nam-en.apc.com/app/answers/detail/a_id/948/