Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Requesting ProLiant ML350 G6 UPS Recommendation
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3003:16 AM. Last Modified: 2024-03-0804:44 AM
Requesting ProLiant ML350 G6 UPS Recommendation
Hello to all forum members and moderators, and thank you in advance for any input you may have.
I am charged with making the correct UPS purchase recommendation for a site that has 3 ProLiant ML350 G6 (tower) server that currently have inadequate power protection. As it stands currently these severs are experiencing power problems that cause them to shut down as opposed to rebooting when certain power events occur. I want to be sure I make the correct recommendation so that I can defend myself with HP support if the problem persists after installing adequate power protection. As these are standalone tower server I will need to specify standalone (not rack mount UPS devices).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3003:16 AM. Last Modified: 2024-03-0804:44 AM
Also the UPS should typically be twice the VA of whatever total you have for devices, so that normally the UPS runs at about 50% load.
Running a UPS at or near 100% load is possible but only gives a runtime of 3-5 minutes, and this is only when the batteries are perfectly fresh and brand new. Average battery lifespan is about 3-4 years, and during this time the runtime will likely decline about 50-70%, meaning a heavily loaded UPS now only runs 1 to 2 minutes. This may not be enough runtime for your devices to shutdown properly.
An alternate way to do it is to size the UPS to exactly match the VA required, and you add an external battery pack to increase the runtime at 100% load.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3003:16 AM. Last Modified: 2024-03-0804:44 AM
Also the UPS should typically be twice the VA of whatever total you have for devices, so that normally the UPS runs at about 50% load.
Running a UPS at or near 100% load is possible but only gives a runtime of 3-5 minutes, and this is only when the batteries are perfectly fresh and brand new. Average battery lifespan is about 3-4 years, and during this time the runtime will likely decline about 50-70%, meaning a heavily loaded UPS now only runs 1 to 2 minutes. This may not be enough runtime for your devices to shutdown properly.
An alternate way to do it is to size the UPS to exactly match the VA required, and you add an external battery pack to increase the runtime at 100% load.