Battery/status problem.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Battery/status problem.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
2
1864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

Battery/status problem.

not exactly sure where to turn here.

I've got a Smart-UPS 3000 that I bought years ago. in 08 I shut it down to move temporarily. A week ago I bought a new #11 cartridge for it from APC. The batteries came in, installed them, and up the UPS came.

But the battery charge lights are blinking constantly. After doing research I'm told it's likely because they don't know what the battery status is since they're new.

I connected using HT to the system that houses the unit and set up the web interface on the card (9606). Got on the web interface, reset the battery install date, ran a self test, and began calibration........

The battery lites stayed blinking but they dropped to one light. After a few hours it charges back up (I assume) but no matter what I do the status shows 'discharged'. I turned off the breaker and let it run with a 39% load. it ran for just over an hour.

Today, for no reason, it just shut off. There's definitely a problem somewhere but I'm not sure what to do. After running the calibration (twice) it says 'passed' but 'unkown' for the date.

I'm very concerned this isn't a good situation. if the UPS doesn't know the status of the batteries how can it know when to stop charging? that's not a good thing. And not only that, there is zero reliability, which is the ONLY reason to have a UPS in the first place right 😞

I'm just frustrated and not sure where to turn. I've done the recommended shut down, disconnect batteries, click and hold the power button and let go on the long beep, but that beep never came. I heard it click off, but that's it. When I plugged it back in, i got a short beep and it just started running. I was holding the button


Any help is greatly appreciated. $350.00 for batteries and I'm bummed this isn't working.

help!!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

how much runtime does the UPS report? and what is the Low-Battery Duration setting at under the Configuration->Shut down parameters section under the UPS section on the left hand side of the screen?

if these values are within two minutes of each other, it may cause this problem. the runtime might not be accurate because the UPS hasnt realized it got a new battery. sometimes a runtime calibration does not fix this issue and we have to try a few other things.

just a guess though.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

I might not have explained this well.

The lights blink, even though they show as charged. it starts at one light, and as it charges the lights increase to 5. but they blink the entire time.

I do know the UPS doesn't know what the status of the batteries are. i just can't figure out how to resolve that. They always show discharged on the status of the web control

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:16 AM . Last Modified: ‎2024-03-08 04:44 AM

how much runtime does the UPS report? and what is the Low-Battery Duration setting at under the Configuration->Shut down parameters section under the UPS section on the left hand side of the screen?

if these values are within two minutes of each other, it may cause this problem. the runtime might not be accurate because the UPS hasnt realized it got a new battery. sometimes a runtime calibration does not fix this issue and we have to try a few other things.

just a guess though.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore