No power being input after switching from utility power to Generator

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • No power being input after switching from utility power to Generator
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
3
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

No power being input after switching from utility power to Generator

Dear all,

I am using Smart-UPS RT 2000VA and when it's connected to the utility power it's working perfectly fine, only thing that the battery is wearing out(almost 3 years). My problem is, when I switch the power source to generator, my UPS unit doesn't receive any power, it has to run on battery.
When I tried to plug in my server direct to the power source which was suppose to connect to the UPS, it works.
I wonder why my UPS doesn't work when the generator is being used in the place of utility power.
please help. Thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

Lights and most motors do not really care too much about the power line frequency. Computers tend to be more sensitive to it.


What is the model/brand of generator? Is there a tachometer on it?

The engine speed regulation may be slightly off, so that results in too high or low frequency which the UPS doesn't like. Engine speed is usually some multiple of 50 or 60 depending on your country.

For example, in the USA, small portable generators commonly spin at 3600 RPM (60 cycles per second * 60 seconds).

The fix may be as simple as slightly increasing or decreasing the engine's governor speed.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

Smart UPS RT are usually very good at running on generator power due to the nature of their design. I'd would check your input voltage and frequency to the UPS with a voltmeter or scope to see if they are okay. Alternatively, if you have software or a network management card installed, you can check in there to see why the UPS is going to battery.

on these models, there is no sensitivity setting like on line interactive smart ups. I'd start with the voltmeter/software/NMC if you have one to see what is going on.

we also have [this article|http://nam-en.apc.com/app/answers/detail/a_id/7354/] but as I mentioned, Smart UPS RT does not have a sensitivity setting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

Thanks for your reply.
the voltage is around 236V, however, I could not find out the frequency.
For your information, all other electrical equipment(air cond, lights etc) are working well with the generator.
Yes, I do have the software connected to the UPC unit, it says power failure, running on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

0 Likes
0
1362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:19 AM . Last Modified: ‎2024-03-08 04:44 AM

Lights and most motors do not really care too much about the power line frequency. Computers tend to be more sensitive to it.


What is the model/brand of generator? Is there a tachometer on it?

The engine speed regulation may be slightly off, so that results in too high or low frequency which the UPS doesn't like. Engine speed is usually some multiple of 50 or 60 depending on your country.

For example, in the USA, small portable generators commonly spin at 3600 RPM (60 cycles per second * 60 seconds).

The fix may be as simple as slightly increasing or decreasing the engine's governor speed.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of