Replacement battery for SUA3000
Hi. We have a Smart-UPS 3000 whose "replace battery" light is on. I'm trying to find the right replacement battery, but the battery selector on the APC site isn't helping. When I type in "SUA3000" as the model number, there's a drop down with nine different model numbers starting with "SUA3000" (e.g. SUA3000R2IX38, SUA3000R3XLNETPKG, SUA3000XLT, etc.), but the one I'm working with is just "SUA3000" (see attached image). I checked all the different models that came up in the battery selector, but there are three different batteries that they take (RBC43, RBC55, and APCRBC105). Does anyone know which battery I need to order?
Thanks.
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:02 AM . Last Modified: 2024-03-15 06:06 AM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:02 AM . Last Modified: 2024-03-15 06:06 AM
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 10:02 AM . Last Modified: 2024-03-15 06:06 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:02 AM . Last Modified: 2024-03-15 06:06 AM
Szabi :
Thanks. I'm not 100% sure if that's the same one, as ours doesn't say "VA" on it anywhere, but the pictures look mostly right (we do have something installed in that slot in the upper left of the back panel, but I don't think that would make a difference).
I think I'll order the 55 and keep my fingers crossed.
Thanks again.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:02 AM . Last Modified: 2024-03-15 06:06 AM
Hi Tim,
The VA in the model's description only indicates the Volt-ampere (power capacity) rating of the UPS, in the same way a W would indicate Watt rating, but as far as the model number sticker goes, that checks out, we only expect to see SUA3000 on that. There is likely a network management card installed in the smartslot - you are right, it doesn't change things from a battery perspective.
Anything else let us know.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-26 01:16 PM
Una consulta, en este modelo APC SUA3000, tengo algunas consultas con respecto a este UPS:
1) La batería resultó correcta la RBC55?
2) El pack de batería se puede armar o si o si debe ser ese pack cerrado?
3) Se pueden cambiar las baterías en caliente?(hotswap)
Gracias!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-27 04:44 AM
1. RBC55 is the correct replacement for that specific model UPS.
2. You can purchase both cartridges or buy the cells individually and assemble.
3. The system is hot swappable.
Questions Ask . . . 👍