Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Regular "Severe - UPS: Bypass not in range; either frequency or voltage"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
3
2537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

Regular "Severe - UPS: Bypass not in range; either frequency or voltage"

We had a lengthy power outage last night and the UPS ran out of battery power. When power returned (about 1 hr after restart) we started getting the error "Severe - UPS: Bypass not in range; either frequency or voltage." (I have a Symmetra 8000 with web card:)

Based on the manual I think I understand the error message. However, the ups event log does not show any over/under voltage or frequency. When I check the current state page of the web interface to the ups, it shows info below. Everything looks fine.

How do I know what the cause of the error is? (Volt or Freq). Is this recorded somewhere? What is the acceptable volt & freq range?

------------------------------

Reason For Last Transfer To Battery: Due to software command or UPS's test control.
Internal Temperature: 037.3 Degrees Celsius
Describes utility power status
Input Voltage: 237.3 VAC
Input Frequency: 59.99 Hz
Maximum Input Voltage: 237.3 VAC
Minimum Input Voltage: 235.6 VAC
Describes output power status
Output Voltage: 234.0 VAC
Output Frequency: 60.00 Hz
Output Current: 00.0 Amps
Output Watts at n+0: 010 %
Output Watts at n+0: 010 %
Output VA at n+0: 007 %
Output VA at n+0: 007 %
Fault tolerance parameters
Redundancy: n+0
Present kVA Capacity: 04.0 kVA
Describes battery status
Battery Capacity: 100.0 %
Runtime Remaining: 0180 Minutes
Nominal Battery Voltage: 120.0 VDC
Actual Battery Bus Voltage: 137.1 VDC
Number of Batteries: 002
Number of Bad Batteries: 000
Self-Test Result: Passed
Self-Test Date: 06/07/2011
Calibration Result: Passed
Calibration Date: 06/03/2011

Message was edited by: ocgltd

Message was edited by: ocgltd

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8000
  • bypass
  • frquency
  • symettra
  • voltage
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
2530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

I widened the freq range to +/ .3 (which MAY solve the problem - but I won't chase this further)
And I turned off drop load on bypass (which caused all my messages)

Thanks!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
2530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

A little more info. I checked the MIM status and see:

state=05 fan=0
100 10 00110101
Vint=244.2 00000000

So input voltage is correctly set to 240v (I think - and why would that change after a full discharge).

The Voltage status shows:

staus
00 Vin Vout Iout
1 237.3 234.0 00.0A

Hopefully there's another clue there for someone knowledgeable.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
2530
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

Here are the settings you asked for:

VoutReport set to AUTO
Output freq set to 60Hz +/- 0.1Hz
Bypass set to "Go to bypass" (was in Drop Load but I just changed it)

So now, how should I interpret these? Should I set VoutReport to 240v? (I have this unit on single phase 240v). Is the output freq too narrow? Does bypass setting matter? etc

I just replaced the SYMIM 2 weeks ago, after the last one died following a power outage. Could this be a factor?

I seem to recall that PowerChute produces a graph of Voltage over time, so I installed Powerchute Business Edition. But PowerChute isn't able to detect the UPS (connected by serial port). I think my Symmetra 8000 is not on the supported device list for Powerchute...is this worth pursuing or is this just incompatable?

Message was edited by: ocgltd

Reply

Link copied. Please paste this link to share this article on your social media post.

ocgltd_apc
Ensign ocgltd_apc
Ensign

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

0 Likes
0
2531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 02:39 AM . Last Modified: ‎2024-03-10 11:13 PM

I widened the freq range to +/ .3 (which MAY solve the problem - but I won't chase this further)
And I turned off drop load on bypass (which caused all my messages)

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore