APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-06-30 02:39 AM . Last Modified: 2024-03-10 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:39 AM . Last Modified: 2024-03-10 11:13 PM
I have a SYA16K16RMP showing 35% load on phase 1 and 72% load on phase 2. I want to balance out the load, but I cannot figure out which outlets on the PDUs on the back are related to which phase? Or if certain PDUs on the back (4 total) are dedicated to a phase 1 while the others are dedicated to phase 2? I read all the manuals I could find, but nothing seemed to mention specifics on that.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:39 AM . Last Modified: 2024-03-10 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:39 AM . Last Modified: 2024-03-10 11:13 PM
I see the two L5-20R outlets on each PDU are balanced between phase 1 and phase 2, but what about the L14-30R outlets?
My goal is just to determine the total load on the UPS to get a general idea of how many more devices/power requirements it can support. I am using 3 of the L14-30R outlets, are those not factored into the readout showing load percentages?
Thanks for your help with this.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:39 AM . Last Modified: 2024-03-10 11:13 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:39 AM . Last Modified: 2024-03-10 11:13 PM
I see the two L5-20R outlets on each PDU are balanced between phase 1 and phase 2, but what about the L14-30R outlets?
My goal is just to determine the total load on the UPS to get a general idea of how many more devices/power requirements it can support. I am using 3 of the L14-30R outlets, are those not factored into the readout showing load percentages?
Thanks for your help with this.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.