Redundancy below alarm threshold (Symmetra 40K THORC456)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Redundancy below alarm threshold (Symmetra 40K THORC456)
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:25 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
9
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:25 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Redundancy below alarm threshold (Symmetra 40K THORC456)

We had a bad power module in our Symmetra 40k. The power module has been replaced, and I cleared out the fault, but the fault keeps coming back.

Now I have the alarm set for "Alarm If Redundancy Under: n+1". Every time we get that alarm, I clear it out, and then it comes back within a day or so. There is never any sign of a failed power module when I login from the web view, and it is always at the correct redundancy of n+1.

How can I troubleshoot this issue to find out what power module is the issue, if any? The logs do not tell you what power module has the problem. The only reason why we knew the other module was failed that we replaced, was because it was off and the fans were not moving...

Can anyone help? Thanks.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Ok...so I got the APC cable and I was able to capture the event log in the Intelligence Module. I see this:

0100A51E IM A Currently there is not power redundancy 04/06/11 12:59:59 478
0100D26E IM D Power Module 2 present 04/06/11 11:37:40 748
0100D51E IM D Currently there is not power redundancy 04/06/11 09:47:06 168
0202A50F PM 02 A Inverter IGBT L1 (Hi) failed 04/06/11 09:15:54 389

Does this mean for Power module #2? I also don't know what the inverter error means...

Please help!

Message was edited by: ekrengel (I attached the full log)

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-26 04:25 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:25 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Can you give us the load information on the unit under two scenarios?

1) When the unit does have the alarm.
2) When the unit does not have the alarm.

Even if it's a small difference, please let us know.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

I can't really tell if the load changes, because every time when I look, the redundancy is back to normal at N+1. I have to clear out the alarm by switching the threshold to "never" and then back to "n+1" again.

If I go to the status view on the LCD screen itself, and watch the redundancy for like a minute or so, it will change to n+0 and then go back to n+1 a couple seconds later.

Is there anyway I can check the logs to see which module this is doing it for? I can't find any specifics...

Message was edited by: ekrengel

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

I have consulted with our three-phase tech support guys and they agree that it's best to check the IM logs on the unit to verify what is generating the redundancy alarm and which PM could still be responsible for the issue. It was highly recommended that you call in for guidance for the procedure, or use an existing service contract to have an FSE dispatched, as improper use of the instructions/commands can affect unit functionality.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Our contract is in the process of getting renewed...So I can't have someone come out just yet.

What are the IM logs? Is there a document I can follow?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Would these be the correct steps?

1. Connect a laptop to the DB-9 connector on either IM module at the top of the UPS frame...
2. Run Hyperterminal at 19200, N,8,1 no flow control.
3. Turn "text capture" on using Transfer --->Capture Text, so you can save your session to a text file.
4. Press Enter, then type "APC" and hit Enter. "___MAIN MENU___" should show up...
5. Type "2" and enter to select "2...Service Inquiry"
6. Type "2", and enter to select menu choice "2. Request Event Log"
7. When its finished, type "0", and enter to Exit
8. Type "9", and enter to select "9. End Service Port Session"
9. You can then stop your text capture.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

I guess a no modem cable won't work ๐Ÿ˜ž

I'm going to have to go buy a male DB-9 connector, all I have is female.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Are you supposed to get a prompt before you type "APC" and hit Enter,

Or will you have a blank page? I was thinking it would be like when you console into a switch, and get a prompt with a welcome page, and at least a cursor...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Is this the only cable that will work with the Intelligence Module?

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=940-0024&tab=models

Everything I've tried hasn't worked...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

0 Likes
0
1483
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-26 04:26 AM . Last Modified: โ€Ž2024-03-19 01:31 AM

Ok...so I got the APC cable and I was able to capture the event log in the Intelligence Module. I see this:

0100A51E IM A Currently there is not power redundancy 04/06/11 12:59:59 478
0100D26E IM D Power Module 2 present 04/06/11 11:37:40 748
0100D51E IM D Currently there is not power redundancy 04/06/11 09:47:06 168
0202A50F PM 02 A Inverter IGBT L1 (Hi) failed 04/06/11 09:15:54 389

Does this mean for Power module #2? I also don't know what the inverter error means...

Please help!

Message was edited by: ekrengel (I attached the full log)

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of