Dc capacitor charge error

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Dc capacitor charge error
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
10
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

Dc capacitor charge error

Hi, our Sl20KHB1 APC ups is displaying "Dc capacitor charge error" is there anything we can quickly do to make it work?
Thanks

Message was edited by: Festronics

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

Hi every one , I am also facing the same problem to our ups am note sure which card I need to replace , and what "TSM" stand for so I can figure it by connections , so if any one have some information I am waiting for your support  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

hi, pls send me phone number, mail or address of any APC engr. here in Nigeria.
thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

Hi, our Sl20KHB1 APC ups is displaying "Dc capacitor charge error" is there anything we can quickly do to make it work?
Thanks

Message was edited by: Festronics

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

Sir, I have fixed the ups by replacing the TSM board.
Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:32 AM

Is this a Silcon UPS? That model number does not come up, even if I try SL20KH1, SI20KH1, etc. Was that the model and serial # right off the white sticker/frame sticker of the unit? Is this a 20kva UPS or not?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

Hi, sorry about the model no- this is the correct model no- SL20KHB1
Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

Ok, this is a 20KW Silcon Unit. I am moving this thread to the Data Center and Facility UPS Forum.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

I've spoken to our three-phase support guys and your best bet is to hit the * key and get a list of all active alarms on the system and call in for support. This error tends to end up requiring some form of service (either actual physical cap or a communication issue). You can call our three-phase support line at 1-800-800-4272; you will be prompted for three-phase technical support. It would be best for you to have the active alarms ready, serial #, model #, and any relevant information on the unit's history.

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

The kind of service you are looking for requires a trained Service Provider or APC FSE. If you have not called in for service yet, we recommend you do so.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1130
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

Hi,Im having the same problem of Capacitor Error not charging,can you please advise on the board you have replaced i.e.TSM board,Im not sure where is this board.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

0 Likes
0
1131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:25 AM . Last Modified: ‎2024-03-19 01:31 AM

Hi every one , I am also facing the same problem to our ups am note sure which card I need to replace , and what "TSM" stand for so I can figure it by connections , so if any one have some information I am waiting for your support  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of