Radius settings not applied when using config.ini on NMC1 and NMC2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Radius settings not applied when using config.ini on NMC1 and NMC2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:01 AM . Last Modified: ‎2024-03-13 01:53 AM

0 Likes
4
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:01 AM . Last Modified: ‎2024-03-13 01:53 AM

Radius settings not applied when using config.ini on NMC1 and NMC2

After uploading a config.ini  with the radius settings below, everything works until the NMC  is rebooted and then you can't log in and must use a paper clip and console cable to allow login  with apc/apc.

I found that after logging in with console cable and checking Radius settings it is prompting me to (8)Accept Changes. After I hit (8) it will say "Successful" and we can then log in with Radius.

If I reset the NMC  to defaults and then upload the config.ini  again and before rebooting it, use the GUI  to "Administration" > "Security" > "RADIUS" > Click the Radius Server and then click "Skip Test and Apply" then I can reboot the NMC  and Radius will work.

Is there a way to "Skip Test and Apply" through the config.ini? 

[SystemRADIUS]
Access=RADIUS, then Local 
PrimaryServer=10.2.160.10
PrimaryServerSecret=xxxxxxxxx
PrimaryServerTimeout=5
SecondaryServer=10.2.160.11
SecondaryServerSecret=xxxxxxxxxxx
SecondaryServerTimeout=5
DNSUpdateInterval=10

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • apply
  • config.ini
  • radius
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

Hi Mike,

I just tried this on a Rack ATS which has the same OS as your PDU. I did not see an issue. What I did was:

  • Push a config.ini with a RADIUS server IP (which is not valid so the NMC should fall back to local auth) and a shared secret
  • Log in using local credentials. Network Management Card (NMC) interface takes noticeably longer to log in, presumably because RADIUS server contact is being tried.
  • Since RADIUS server IP is not reachable, NMC falls back to using local authentication.
  • Reboot and repeat process. Able to log in.

But I am interested to see if you can confirm any of my other questions to make sure I am truly simulating the same thing. 

I also re-tried with my online RADIUS server but the problem I have is it is FreeRADIUS and my database is messed up so I can't authenticate users properly. I can get it to hit the RADIUS server though and tell me invalid username and password. Same through serial until I unplug the network cable so it falls back to local authentication with the network being disconnected and I can log in through local authentication.

I logged in via serial after a reboot and the RADIUS server settings are still there and it does not show as pending changes on the RADIUS config screen.

Does anything sound majorly different to you compared to what you did? From all my testing, it seems as though the test is being skipped.

If you don't notice anything crazy, I will also test with my Rack PDU to be safe, though I don't think it will be different. It is just more difficult for my to serial into based on where I have it installed laughing

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

Hi Mike,

What firmware(s) did you try this on? I just tried what I think you did on NMC2 AOS 6.4.0 and didn't have a problem. My only possible difference is my NMC fell back to local authentication before and after reboot (successfully) because I don't have a working RADIUS server set up right this second. But, based on what you said, I assume that didn't work for you either if you had to get the paper clip out. I am also assuming you at some point tried credentials that are in the local database before going the serial access route as a last resort.

And when you are getting the serial cable out using apc/apc - are those the local database credentials you've left at default or what you're using as part of the password reset procedure?

What you've described as far as menus and behavior sounds just like NMC1 only but this does happen for you on NMC2 as well as mentioned in the title of the question? (or, it could be NMC2 older firmware too)

Once I know the NMC1 firmware, I can check further potentially on one of those devices as well as the intended behavior of our systems in general.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

Hello! This is on an AP7801 running what I thought was the latest firmware. 

Name: rpdu
Version: v3.7.4
Date: 03/13/2012
Time: 16:16:54

Name: aos
Version: v3.9.0
Date: 05/11/2015
Time: 14:45:05

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

0 Likes
0
1548
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

Hi - yes, that's the latest and that device is an NMC1. I'll give it a try with one of these tomorrow.

You had also tested this on an NMC2?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

0 Likes
0
1549
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:02 AM . Last Modified: ‎2024-03-13 01:53 AM

Hi Mike,

I just tried this on a Rack ATS which has the same OS as your PDU. I did not see an issue. What I did was:

  • Push a config.ini with a RADIUS server IP (which is not valid so the NMC should fall back to local auth) and a shared secret
  • Log in using local credentials. Network Management Card (NMC) interface takes noticeably longer to log in, presumably because RADIUS server contact is being tried.
  • Since RADIUS server IP is not reachable, NMC falls back to using local authentication.
  • Reboot and repeat process. Able to log in.

But I am interested to see if you can confirm any of my other questions to make sure I am truly simulating the same thing. 

I also re-tried with my online RADIUS server but the problem I have is it is FreeRADIUS and my database is messed up so I can't authenticate users properly. I can get it to hit the RADIUS server though and tell me invalid username and password. Same through serial until I unplug the network cable so it falls back to local authentication with the network being disconnected and I can log in through local authentication.

I logged in via serial after a reboot and the RADIUS server settings are still there and it does not show as pending changes on the RADIUS config screen.

Does anything sound majorly different to you compared to what you did? From all my testing, it seems as though the test is being skipped.

If you don't notice anything crazy, I will also test with my Rack PDU to be safe, though I don't think it will be different. It is just more difficult for my to serial into based on where I have it installed laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore