Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Proper Power Cable
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2809:48 PM. Last Modified: 2024-03-1411:36 PM
Proper Power Cable
I'm looking to add a APC Smart-UPS RT 6000VA 208V into the mix at my data center. It's going to be holding up a load of about 11amps (1500w) at max. Normally this thing would be plugged into it's own L6-30R socket. Since those are occupied where it's going, I'd like to plug it into a C20 with a max of 15 A @208 (basically on a APC PDU). What will my issues be? (Note - this is all hypothetical.) Will the unit immediately draw too much power for this source, for instance, while recharging batteries?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2809:48 PM. Last Modified: 2024-03-1411:36 PM
Hello:
There won't technically be any problems doing this, other than the obvious de-rating. Some quick math will tell you that this will give you a maximum draw of 3120 VA; this is excluding any local codes, though, which may vary depending on your area. The battery charger wattage on this unit is 421W, so shouldn't have a huge impact.
If you are sticking to the 11a load as you say, you may be ok, but must keep inrush current in mind. Consider the worst case scenario in your sizing (i.e. all servers powering up at once). Again, also keep local electrical codes in mind.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2809:48 PM. Last Modified: 2024-03-1411:36 PM
Hello:
There won't technically be any problems doing this, other than the obvious de-rating. Some quick math will tell you that this will give you a maximum draw of 3120 VA; this is excluding any local codes, though, which may vary depending on your area. The battery charger wattage on this unit is 421W, so shouldn't have a huge impact.
If you are sticking to the 11a load as you say, you may be ok, but must keep inrush current in mind. Consider the worst case scenario in your sizing (i.e. all servers powering up at once). Again, also keep local electrical codes in mind.