Problems when connection of the load APC Smart-UPS 5000VA XLI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problems when connection of the load APC Smart-UPS 5000VA XLI
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:17 PM

0 Likes
8
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:17 PM

Problems when connection of the load APC Smart-UPS 5000VA XLI

Good morning,

I have a Smart-UPS APC SURTD5000XLI, the ups work normally when no load is connected, the leds on the front display is fixed.

When I try to connect a load the status bar battery starts flashing, anyone have any idea what can be? Have been replaced batteries.

Thank u!!

Fabrizio

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • apc5000
  • smartups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

Your state of charge needs to be 100% (it is) and there need at least 30% load (there isn't) for the UPS to do a runtime calibration. Load must not vary significantly while calibration is running.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:17 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:26 AM . Last Modified: ‎2024-03-18 11:17 PM

Hi Fabrizio,

Based on your description, I would take a look at this kbase (FA156538) - http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US〈=en&i...

I'm thinking that when you add load, the UPS doesn't have enough runtime (or doesn't think it has enough runtime) to adequately support the load for a long enough time. We would want to know how much load you are adding, how much runtime the UPS thinks it has, and what your low battery threshold is set at.

If you have different symptoms or the kbase doesn't help, we would like to see the logs from your network management card in the UPS (search for FA156131) and a picture of your UPS display if possible.

Thanks,

Tommy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

Hi,

The screenshots show that without load the UPS has 42 minutes 14 seconds of runtime. With load the runtime drops to 21 seconds. That is insufficient time to power down a computer system. You should read Kbase FA156538 “Why are the battery charge LEDs flashing on a Smart-UPS?” If the batteries are new you should perform a runtime calibration as described in the Kbase. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

Hi Bill,

I performed the manual runtime calibration with about 15% of load, when the battery is at 100% I performed a self-test and the charger battery leds start flashing again and the run time is about 2 minutes!

Can I try to replace the battery carriage?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

Hi,

If the batteries are not new then yes, replacing the batteries should help. The unit with no load should show hours of available runtime not 42 minutes. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:17 PM

Hi,


I have replaced the battery carriage but immediately the charger battery leds started flashing again!

If I do a self-test, same event, battery leds flashing and "bip bip bip bip"...

At the moment I keep the batteries with the connected load and I check tomorrow.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

Hi Fabrizio,

Sorry to hear you are having more issues.

A few questions-

What is the runtime listed in the network card now that you replaced the batteries and let them charge?

Did you replace these batteries with genuine APC ones (if so, what's the serial number on it) or third party batteries?

Do you have external batteries connected (and if so, did you replace those as well)? I see in the screenshot none were configured, but I figured I would ask.

If the estimated runtime is still the same and you replaced the batteries with genuine ones, I would recommend a runtime calibration. Instructions are in the kbase listed before.

Thanks,

Tommy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

Hi Tommy,

the runtime remaning is the same:

uVLz3vbrugN7JbgFKs%2Fp8g%3D%3D.jpeguVLz3vbrugN7JbgFKs%2Fp8g%3D%3D.jpeg

If I try a runtime calibration, the ups refused this action:

0rvrLjxsPWpSY4w3Bsi%2BEA%3D%3D.jpeg0rvrLjxsPWpSY4w3Bsi%2BEA%3D%3D.jpeg

I have replaced the batteries only with genuine APC ones and there are not external batteries connected on the ups.

Wait for your response, thanks

Fabrizio

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

0 Likes
0
1380
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:27 AM . Last Modified: ‎2024-03-18 11:16 PM

Your state of charge needs to be 100% (it is) and there need at least 30% load (there isn't) for the UPS to do a runtime calibration. Load must not vary significantly while calibration is running.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of