Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:14 AM
Se me presento este inconveniente después de actualizar el firmware del AP9630. El mismo no muestra el estado de las baterías, ni tampoco el valor de carga, y demás datos de Inicio. Esto afecta a las distintas alarmas, dado que no registra esto tampoco registra alarmas.
.
Seria de mucha ayuda, saber como proseguir o ver de solucionar este inconveniente.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:13 AM
La versión de firmware de su AP9630 tarjeta de administración de red es incorrecta. El nombre del módulo de firmware, 'sy3p' es para los modelos trifásicos Symmetra. Tiene un modo de Smart-UPS. Usted necesita actualizar su firmware a la versión correcta.
Refiérase a http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ap9630&tab=software y tendrás SFSUMX611. Las instrucciones sobre la actualización de firmware se encuentran aquí -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:14 AM
Hola,
¿QuéUPSModelotienes?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:14 AM
El Modelo del Equipo es SRC3000XLI
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:13 AM
La versión de firmware de su AP9630 tarjeta de administración de red es incorrecta. El nombre del módulo de firmware, 'sy3p' es para los modelos trifásicos Symmetra. Tiene un modo de Smart-UPS. Usted necesita actualizar su firmware a la versión correcta.
Refiérase a http://www.apc.com/resource/include/techspec_index.cfm?base_sku=ap9630&tab=software y tendrás SFSUMX611. Las instrucciones sobre la actualización de firmware se encuentran aquí -> How do I upgrade the firmware on an APC Network Management Card? | FAQs | Schneider Electric US
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:13 AM
Gracias Angela. Instale el Firmware que me indicaste y funciona todo de 10.
Y queria consultarte si este firmware funciona para todos los modelos Smart-UPS Mónofasicos
Saludos
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:13 AM
De nada. Sí, en realidad este firmware funciona para nada llamado Smart-UPS. La mayoría de los Smart-UPS son una sola fase, pero Smart-UPS VT es de 3 fases y utiliza este firmware también. Galaxy 3500 también utiliza este firmware, ya que es básicamente un VT Smart-UPS.