Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

PowerChute PE is not saving energy cost.

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute PE is not saving energy cost.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
azbruno_apc
Ensign azbruno_apc
Ensign

Posted: ‎2021-07-01 05:46 AM

0 Likes
2
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:46 AM

PowerChute PE is not saving energy cost.

This was originally posted on APC forums on 5/24/2014


Running PCPE 3.0.2. I enter a new value for the energy cost and it is good until the next time I boot Windows. Then it's back to the default ($.10). Shouldn't it be saved? Can someone tell me where it would be saved?

Thanks.

-Bruno

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
azbruno_apc
Ensign azbruno_apc
Ensign

Posted: ‎2021-07-01 05:46 AM

0 Likes
0
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:46 AM

This was originally posted on APC forums on 5/27/2014


I ended up turning off the Data Service. When I looked at the EnergyLog.mdb contents, it looked like it was adding entries in the CurrentEnergyUsage table at a very high frequency... far more than I cared for, especially since I'm using an SSD for the C: drive. The EnergyUsageLog (one entry per day), looks OK.

I find there are three files that are stored in the Program Files folder which should really be located in the ProgramData folder (or AppData). One of them, eventlog.dat, can be moved to another location via the PCPE UI, but the other two, PCPELog.txt and EnergyLog.mdb, cannot be moved. And unfortunately, eventlog.dat can't be read due to unknown format.

Anyway, my new unit is completely failing to properly power the controlled outlets when the Energy Management feature is enabled (always powered off, regardless of conditions), so APC is sending me a new unit. When that arrives, I'll uninstall PCPE and then reinstall, to the 😧 drive. Unless I go with APCUPSD instead.

-Bruno

See Answer In Context

Reply
Share
Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:46 AM

0 Likes
0
220
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:46 AM

This reply was originally posted by Anonymous on APC forums on 5/27/2014


Hello,

Yes, this should be saved in the Energylog file. I suspect that there is a corruption on the DB.

I replicated the issue you are seeing by corrupting the DB. To fix the issue I uninstalled and then reinstalled PCPE.

Let me know if this fixes your issue.

Regards,

B

Reply
Share
azbruno_apc
Ensign azbruno_apc
Ensign

Posted: ‎2021-07-01 05:46 AM

0 Likes
0
221
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 05:46 AM

This was originally posted on APC forums on 5/27/2014


I ended up turning off the Data Service. When I looked at the EnergyLog.mdb contents, it looked like it was adding entries in the CurrentEnergyUsage table at a very high frequency... far more than I cared for, especially since I'm using an SSD for the C: drive. The EnergyUsageLog (one entry per day), looks OK.

I find there are three files that are stored in the Program Files folder which should really be located in the ProgramData folder (or AppData). One of them, eventlog.dat, can be moved to another location via the PCPE UI, but the other two, PCPELog.txt and EnergyLog.mdb, cannot be moved. And unfortunately, eventlog.dat can't be read due to unknown format.

Anyway, my new unit is completely failing to properly power the controlled outlets when the Energy Management feature is enabled (always powered off, regardless of conditions), so APC is sending me a new unit. When that arrives, I'll uninstall PCPE and then reinstall, to the 😧 drive. Unless I go with APCUPSD instead.

-Bruno

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc