I have a ESX 5.1 host with the PCNS virtual appliance installed. The virtual appliance is connected with the network management card.
It is configured to communicate with virtual center.
On one of the vm's runs a database, this database needs to be stopped before shutting down the vm. Do I need to install a agent in the vm to run a batch file to stop the database in case of a power failure?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:22 AM
Hi,
You could install a PCNS agent in the VM or use a customized VMware tools script to shut down the database (before shutting down the Guest). Using the shutdown command file won't work because VM shutdown is triggered before the command file is executed in the shutdown sequence.
See this link on using custom VMware Tools scripts vSphere Documentation Center
Or you could configure an Event Driven command file via PCNS to trigger the database shutdown before the main shutdown sequence starts - go to Configure Events page, select Run Command action Here you can add the script to trigger the database shutdown after a delay value in seconds - you'd need to work out how long it takes for the DB to shut down and maybe increase the shutdown delay for the On Battery event to allow enough time for the script to run.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 05:46 AM . Last Modified: 2024-03-05 12:22 AM
Hi,
You could install a PCNS agent in the VM or use a customized VMware tools script to shut down the database (before shutting down the Guest). Using the shutdown command file won't work because VM shutdown is triggered before the command file is executed in the shutdown sequence.
See this link on using custom VMware Tools scripts vSphere Documentation Center
Or you could configure an Event Driven command file via PCNS to trigger the database shutdown before the main shutdown sequence starts - go to Configure Events page, select Run Command action Here you can add the script to trigger the database shutdown after a delay value in seconds - you'd need to work out how long it takes for the DB to shut down and maybe increase the shutdown delay for the On Battery event to allow enough time for the script to run.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.