Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Need a agent in the VM
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0105:46 AM. Last Modified: 2024-03-0512:22 AM
Need a agent in the VM
I have a ESX 5.1 host with the PCNS virtual appliance installed. The virtual appliance is connected with the network management card. It is configured to communicate with virtual center. On one of the vm's runs a database, this database needs to be stopped before shutting down the vm. Do I need to install a agent in the vm to run a batch file to stop the database in case of a power failure?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0105:46 AM. Last Modified: 2024-03-0512:22 AM
Hi,
You could install a PCNS agent in the VM or use a customized VMware tools script to shut down the database (before shutting down the Guest). Using the shutdown command file won't work because VM shutdown is triggered before the command file is executed in the shutdown sequence.
Or you could configure an Event Driven command file via PCNS to trigger the database shutdown before the main shutdown sequence starts - go to Configure Events page, select Run Command action Here you can add the script to trigger the database shutdown after a delay value in seconds - you'd need to work out how long it takes for the DB to shut down and maybe increase the shutdown delay for the On Battery event to allow enough time for the script to run.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0105:46 AM. Last Modified: 2024-03-0512:22 AM
Hi,
You could install a PCNS agent in the VM or use a customized VMware tools script to shut down the database (before shutting down the Guest). Using the shutdown command file won't work because VM shutdown is triggered before the command file is executed in the shutdown sequence.
Or you could configure an Event Driven command file via PCNS to trigger the database shutdown before the main shutdown sequence starts - go to Configure Events page, select Run Command action Here you can add the script to trigger the database shutdown after a delay value in seconds - you'd need to work out how long it takes for the DB to shut down and maybe increase the shutdown delay for the On Battery event to allow enough time for the script to run.