Problem with SMT1500RMI2U 1500VA - message when UPS turned on "EPO Active - Press On/Off Key"

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Problem with SMT1500RMI2U 1500VA - message when UPS turned on "EPO Active - Press On/Off Key"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:25 AM

0 Likes
6
6100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:25 AM

Problem with SMT1500RMI2U 1500VA - message when UPS turned on "EPO Active - Press On/Off Key"

Hi, 

So registered here with the hope I might be able to find a solution to this problem.

I recently bought an APC SMT1500RMI2U from ebay sans batteries, bought some batteries for the unit and it seemed to be working fine.

Then after several hours of operation the unit would turn off with a message about "Relay Weld" - I found someone else who had this and replaced all of the replays on the circuit boards. I did the same and this problem went away. (The eBay seller refunded me an agreed amount, so I paid very little for it on the principle of it being 'for parts' - so I am not too sour about this if I end up having to bin it)

Unfortunately I am now presented with a new problem. 

When attaching the unit to power the message "EPO Active - Press On/Off Key" comes up - this happens both when plugged into mains or running from batteries. I have managed to get it to go away a couple of times after leaving the unit unplugged from mains and battery for a while and then plugging back in (I think this is referred to as 'braindeading' the unit). However this is not working at the moment.

The unit does not have an EPO connector on the back so it is not possible to activate the EPO externally.

My (uneducated) guess at what is happening is that the internal circuitry in these units is standardised and somewhere on the circuit board is the point where the 'EPO switch' would be connected and there is some kind of short circuit going on at this point.

I basically just wanted to ask before I open her back up if anyone has seen this kind of fault before or if they are able to offer me any kind of direction in terms of where to look for faults?

Cheers,

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:25 AM

0 Likes
0
6100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:25 AM

Just bumping this to see if anyone has any ideas as I haven't been able to solve the problem.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
6100
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:24 AM

Hello,

We are experiencing the same issue with one of SMC3000RML units. Working fine for nearly a year and then this appears.

The LCD screen shows EPO Active - Press On/Off Key

Pressing the on/off key does nothing, the unit beeps but the LCD does not change and the unit does nothing.

I installed the PowerChute software and connected with my laptop. The software connects, nothing much in the event log of it. I try to run a self-diagnostics test, it runs for 2-3 seconds then in the results section of the test it says "Refused". Never had that happen before.

I was inquiring if you ever found a resolution, besides chucking the unit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:25 AM

0 Likes
0
6101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:25 AM

Just bumping this to see if anyone has any ideas as I haven't been able to solve the problem.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:24 AM

0 Likes
0
6101
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:30 AM . Last Modified: ‎2024-03-18 12:24 AM

Hello,

We are experiencing the same issue with one of SMC3000RML units. Working fine for nearly a year and then this appears.

The LCD screen shows EPO Active - Press On/Off Key

Pressing the on/off key does nothing, the unit beeps but the LCD does not change and the unit does nothing.

I installed the PowerChute software and connected with my laptop. The software connects, nothing much in the event log of it. I try to run a self-diagnostics test, it runs for 2-3 seconds then in the results section of the test it says "Refused". Never had that happen before.

I was inquiring if you ever found a resolution, besides chucking the unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

JPL-Mike
JPL-Mike
Cadet

Posted: ‎2024-03-26 10:36 AM

0 Likes
1
4309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-03-26 10:36 AM

Hello All,

I am also dealing with this issue with two new APC units

Model
Smart-UPS X 2000

SKU-SMX2000RMLV2UNC

I have tired everything to get this to clear and nothing works. I had one device connected to it, ran for 2 days then got this error when I came in the other morning. I couldnt get it to clear, replaced it with another main unit and connected everything the same got the same issue a few days later. Would it be the power input that might be causing this issue. Its connected to a 110v outlet with the correct amp rating and circuit breaker. This is really concerning as i have like 4 more of these units that I need to deploy but not with this issue.

 

I tired disconnecting the battery, try another outlet/circuit, updating firmware, running on battery only, still same issue. Note there is no EOP wired up or anything for this to trigger, i even tried wiring in a push button to the EOP input on the back, it didnt do anything on any of the terminal position. Really need help on this ASAP.

 

I also tried to perform the self test as mention above and got the same results.

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2024-04-02 07:45 AM

In response to JPL-Mike
0 Likes
0
4262
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-04-02 07:45 AM

If these units are brand new I would highly suggest you reach out to APC Technical Support directly and request a RMA. 

In the interim what does the internal logs show? What are the serial numbers of the units showing this problem?!?

 

Lastly, please upload a photo of the EPO message displayed on the LCD when present.

Reply

Link copied. Please paste this link to share this article on your social media post.

ManDuong
ManDuong
Cadet

Posted: ‎2024-05-17 12:01 AM

0 Likes
0
3958
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-17 12:01 AM

Hi,

I have the same your issue with UPS model: SRT10KRMXLI

I tried download new firmware version at apc website:

https://www.apc.com/vn/en/download/software-firmware/

After run update new firware from browser, i can turn off EPO & turn on the outlets group

Now it working ok

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

ABBman213
ABBman213
Cadet

Posted: ‎2024-08-21 06:22 AM

0 Likes
0
3257
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-08-21 06:22 AM

Hello I just spent a day troubleshooting a smx3000rmhv2unc for the same "EPO Activate press on/off" I finally found the solution. My emergency power off relay was normally open. We had common running to pin 3 and +24vDC to pin 1 jumpered to pin 2. This was the configuration for normally closed contacts. If you switch +24VDC to pin 1, no jumper required and common to pin 2 you will be able to cycle power on off with the button, clearing the EPO fault.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore