I am looking in the software section for my SMT750 and found this one
Network Management Card v5.0.1 firmware executable for Smart UPS AP9630/31
My management card is a AP9630 so this looks right.
Where in the UPS do I find my current version? (using web browser?)
I think I have 5.0 now so would this be worth the upgrade?
Thanks - new to the firmware updates.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 01:36 AM . Last Modified: β2024-03-06 01:32 AM
the latest firmware version for AP9630/AP9631 is 5.1.7. Version 5.0.1 is ancient and should not be used.
to check your current firmware version, log in to the web UI and go to administration tab->General->About. i'd highly recommend you update if it is not 5.1.6 at the minimum. we have introduced many new features and bug fixes since 5.0.1 and you'd be missing out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2021-07-01 01:36 AM . Last Modified: β2024-03-06 01:32 AM
the latest firmware version for AP9630/AP9631 is 5.1.7. Version 5.0.1 is ancient and should not be used.
to check your current firmware version, log in to the web UI and go to administration tab->General->About. i'd highly recommend you update if it is not 5.1.6 at the minimum. we have introduced many new features and bug fixes since 5.0.1 and you'd be missing out.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-08-20 11:59 AM
Where can I find the version 5.1.7? I have some devices that need to have the firmware "stair stepped" as to not lose my configurations.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-08-21 05:10 AM
5.1.7 is latest version for AP9630? Then why do I have v7.1.6 running on my cards?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-08-21 07:08 AM
That specific answer and posting was in 2021. The other member is requesting the same version of firmware to allow a stepped upgrade.
Doing so reduces the possibility of corrupting the NMC. v7.1.6 is the latest firmware release for the NMC 2 card. π