I am trying to troubleshoot why PowerchuteVM only shutdown the VMware host on which is running.
Here is my environment.
- Smart-UPS X 3000
- 3 VMwareHost
- VCenter Server Appliance running on ESXI 03
- PCNS 4.3 running as a VM on ESXI 03
Here is the log
| 07/14/2019 | 19:34:32 | Available runtime is sufficient. |
| 07/14/2019 | 19:16:21 | Powering on VMs on Host 10.0.1.40. |
| 07/14/2019 | 19:16:21 | Powering on VMs on Host esxi04.domain.com. |
| 07/14/2019 | 19:16:20 | Powering on VMs on Host esxi03.domain.com. |
| 07/14/2019 | 19:15:29 | vCenter Server is accessible. PowerChute will be able to issue commands to Virtual Machines or Hosts. |
| 07/14/2019 | 19:13:41 | Available runtime has been exceeded. |
| 07/14/2019 | 19:13:41 | Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts. |
| 07/14/2019 | 19:13:14 | PowerChute successfully opened TCP port 6547. |
| 07/14/2019 | 19:13:14 | PowerChute successfully opened TCP port 3052. |
| 07/14/2019 | 19:13:14 | PowerChute is attempting to open TCP port 3052. |
| 07/14/2019 | 19:13:14 | PowerChute is attempting to open TCP port 6547. |
| 07/14/2019 | 19:13:13 | PowerChute Network Shutdown version 4.3.0 monitoring started. |
| 07/14/2019 | 19:13:11 | Communication established with Environmental Monitor. |
| 07/14/2019 | 19:13:11 | Communication has been established. |
| 07/14/2019 | 19:12:44 | PowerChute successfully opened UDP port 3052. |
| 07/14/2019 | 19:12:44 | PowerChute is attempting to open UDP port 3052. |
| 07/14/2019 | 17:11:07 | Shutdown Host failed for Host esxi03.domain.com. |
| 07/14/2019 | 17:10:47 | Shutdown Host failed for Host esxi04.domain.com. |
| 07/14/2019 | 17:10:27 | Shutdown Host failed for Host 10.0.1.40. |
| 07/14/2019 | 17:06:17 | Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts. |
| 07/14/2019 | 17:06:17 | Maintenance Mode Task cancelled on Host esxi03.domain.com as VCSA VM is shutting down. |
| 07/14/2019 | 17:06:16 | Shutting down vCenter Server VM VMVCSA01. |
| 07/14/2019 | 17:04:35 | Host 10.0.1.40 has successfully entered Maintenance Mode. |
| 07/14/2019 | 17:03:55 | Host esxi04.domain.com has successfully entered Maintenance Mode. |
| 07/14/2019 | 17:03:05 | Exit Maintenance Mode on Host esxi03.domain.com. |
| 07/14/2019 | 16:52:10 | UPS critical event: Outlet Group Turn off initiated. |
| 07/14/2019 | 16:52:10 | UPS Outlet Group: vCenter-Hosts turn off has been initiated. |
| 07/14/2019 | 16:52:05 | Shutting down VMs on Host esxi03.domain.com. |
| 07/14/2019 | 16:52:05 | Starting Maintenance Mode Task on Host esxi03.domain.com. |
| 07/14/2019 | 16:52:05 | No vApp to shutdown on Host esxi04.domain.com. |
| 07/14/2019 | 16:52:05 | Starting vApp shutdown process. |
| 07/14/2019 | 16:52:05 | Shutting down VMs on Host 10.0.1.40. |
| 07/14/2019 | 16:52:05 | Starting Maintenance Mode Task on Host 10.0.1.40. |
| 07/14/2019 | 16:52:04 | Shutting down VMs on Host esxi04.domain.com. |
| 07/14/2019 | 16:52:04 | Starting Maintenance Mode Task on Host esxi04.domain.com. |
| 07/14/2019 | 16:52:04 | PowerChute is turning off UPS 10.0.1.10 |
| 07/14/2019 | 16:52:04 | Shutdown sequence started on Hosts esxi03.domain.com, 10.0.1.40, esxi04.domain.com in response to UPS critical event: On Battery. |
| 07/14/2019 | 16:52:04 | UPS critical event: On Battery. |
| 07/14/2019 | 16:50:04 | UPS has switched to battery power. |
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:29 PM . Last Modified: 2024-02-14 11:53 PM
Hi,
I have reviewed the logs and configuration file. I can see where the start up of High, Medium, Low are being executed. I do not see a success response for all however. I also see that most all VMs for host esxi03 remained listed in the file store properties file.
I am sending the files to a colleague and will post back when I have more info.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hello,
The log indicates there may be a permissions issue happening. When vCenter is running PCNS will communicate with the host through vCenter. Once vCenter go off line PCNS must communicate directly with the host. See page 62 of the User's Guide for assistance with creating local account that PCNS will use to communicate with he hosts.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hi Bill,
I did not add VCenter to any priority group in VM Prioritization , do you think this could be the issue.
Before the Test , I created the local user on 3 hosts and VCenter.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hi,
On 7/24/2019 12:00 PM, Juan said:I did not add VCenter to any priority group in VM Prioritization , do you think this could be the issue.
No. vCenter is being powered down
| 07/14/2019 | 17:06:16 | Shutting down vCenter Server VM VMVCSA01. |
The issue is PCNS cannot shutdown the host
| 07/14/2019 | 17:11:07 | Shutdown Host failed for Host esxi03.domain.com. |
| 07/14/2019 | 17:10:47 | Shutdown Host failed for Host esxi04.domain.com. |
if the issue is not permissions have you reviewed the error.log to see what may have caused the issue. Troubleshooting host failed to power down is listed in the troubleshooting section of the User's Guide. VMware troubleshooting starts on page 179.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Bill,
I changed the PowerchuteNS to a physical Server, all 3 host are shutting down successfully.
Now when I restored the power , all servers turn on correctly, but only one host is able to exit out of maintenance mode, and no VMs are power on.
I attached the logs.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hello,
The log shows there is a DNS configuration issue preventing PowerChute from connecting to the host e.g. a stale DNS record containing an invalid hostname/FQDN or IP address. VI SDK invoke exception:java.net.UnkownHostException
ON the Windows system add the host names and IP addresses to the etc/hosts file
The file will be found at C:\Windows\System32\drivers\etc
Below is an example of a file that I have edited and added to hosts to the file.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Do I need to add the VCSA dns name to the etc/host file ?
I removed the entries on VirtualizationFileStore.properties
Thank you
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hi,
You can add that info to allow PCNS to communicate with vCenter in the event that DNS is off line.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hi Bill,
I did two tests, the 3 hosts out of maintenance mode successfully. But at the moment to power on VMs from Prioritize groups some VMs wont power on. When I did the first test there were more VMs off from 2 hosts, in the second test only some VMs from one host couldn't power on automatically.
Check the logs please
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
Hi,
According to the event log everything looks to have started properly.
08/04/2019 11:04:13 Exit Maintenance Mode on Host mx-esxi03.kwalu.com. .3.4.9.9
08/04/2019 11:04:19 Exit Maintenance Mode on Host 10.0.7.40. .3.4.9.9
08/04/2019 11:04:20 Exit Maintenance Mode on Host mx-esxi04.kwalu.com. .3.4.9.9
08/04/2019 11:05:08 Powering on VMs on Host mx-esxi04.kwalu.com. .3.4.9.9
08/04/2019 11:05:08 Powering on VMs on Host mx-esxi03.kwalu.com. .3.4.9.9
08/04/2019 11:05:08 Attempting to start vCenter Server VM MX-VMVCSA01. .3.4.9.9
08/04/2019 11:05:08 Powering on VMs on Host 10.0.7.40. .3.4.9.9
May I have an updated copy of the pcnsconfig.ini file and a copy of the VirtualizationFileStore.Properties file. Also, do you know what VMs where powered on when the shutdown process started?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:29 PM . Last Modified: 2024-02-14 11:53 PM
Hello Bill,
I see this error on error.txt (previous attached file) .
2019-08-04T11:13:29,520 ERROR pool-36-thread-2 com.apcc.m11.components.Shutdowner.VMStartupRunnable java.rmi.RemoteException: An error occurred getting a response from the connection at url https://host1:443/sdk; nested exception is:
java.net.SocketTimeoutException: Read timed out
at com.vmware.vim25.ws.WSClient.getInputStreamFromConnection(WSClient.java:201) - performVMStartUp() - RemoteException:
Also I attached the pcnsconfig and virtual properties.
Only VMs not included on High Group wont powered on in Host 1, Host 2 and Host 3 all VMs sucessfully powered on and somes VMs are Medium and Low groups.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:29 PM . Last Modified: 2024-02-14 11:53 PM
Hi,
I have reviewed the logs and configuration file. I can see where the start up of High, Medium, Low are being executed. I do not see a success response for all however. I also see that most all VMs for host esxi03 remained listed in the file store properties file.
I am sending the files to a colleague and will post back when I have more info.
Link copied. Please paste this link to share this article on your social media post.