Hi,
I have a couple of questions:
Thanks! Ray
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
1- If you set a 0 second duration for a priority group, the migration action will be skipped for all VMs in that priority group.
2- Waits 120 seconds even if the task finished before or later. Then starts the next group depending if its migrating , shutdown or starting.
3- I used the Youtube channel for some configuration and the user guide for PCNS 4.3
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 11:28 PM . Last Modified: 2024-02-14 11:53 PM
1- If you set a 0 second duration for a priority group, the migration action will be skipped for all VMs in that priority group.
2- Waits 120 seconds even if the task finished before or later. Then starts the next group depending if its migrating , shutdown or starting.
3- I used the Youtube channel for some configuration and the user guide for PCNS 4.3