At the risk of sounding like I've had my brain removed, I'm assuming that Powerchute Network Shutdown needs to be installed on each server I want to shutdown when events occur?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:01 AM . Last Modified: 2024-02-29 11:37 PM
Keith,
Fair question. It depends on the environment. If the servers are stand-alone then yes you would install on each server. If the servers are hosts of other virtual machines than it depends on the configuration.
Examples:
6 server running Windows 2012 R2 = install on each system
6 ESXi hosts not managed by vCenter Server = install PCNS appliance on each host
6 ESXi host managed by vCenter Server = install PCNS appliance once
We have application note 180 that discusses VMware ESXi options.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:01 AM . Last Modified: 2024-02-29 11:37 PM
Keith,
Fair question. It depends on the environment. If the servers are stand-alone then yes you would install on each server. If the servers are hosts of other virtual machines than it depends on the configuration.
Examples:
6 server running Windows 2012 R2 = install on each system
6 ESXi hosts not managed by vCenter Server = install PCNS appliance on each host
6 ESXi host managed by vCenter Server = install PCNS appliance once
We have application note 180 that discusses VMware ESXi options.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:02 AM . Last Modified: 2024-02-29 11:37 PM
Thanks Bill. The servers are all standalone