Datacenter, Symmetra and PCNSD

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Datacenter, Symmetra and PCNSD
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
123
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

0 Likes
3
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

Datacenter, Symmetra and PCNSD

Hello all!!!

I just got my first datacenter up and running.  We have 2 hosts, shared storage and a APC Symmetra.  I have the PCNSD ova installed in my cluster and it is talking to my APC.  I went through the setup and basically stuck with the defaults on how to handle the VMs.  My UPS says it will run for 40min on battery.  I would like to start the process of a shutdown at 10min (25%) run time left.  The settings on the device (APC) and the appliance have me a little confused.  Maybe someone could help me out?

This is how my APC is configured:

Start of Shutdown

Low Battery Duration = 10 mins

Shutdown Delay = 20secs

Basic Signaling = Enabled

PowerChute Shutdown Parameters

Max Req Delay = 10 min

Now in my PCNS server:

Shutdown Settings:

Dont turn off UPS

VM settings

Dont Migrate

VM Shutdown 120 secs no start up

vCenter Shutdown 240 secs

In Configure Events in PCNS and Im thinking I need to set Runtime remaining below thresholds Shutdown settings.  When you enable that it alows you to edit the Threshold.  What is this threshold?  Is it not listening to the 10min that I set on  the UPS?  Is this in addition to that?  Do I set that to 600 (10x60) ?  Its not very clear what that is.

Do my PCNS and UPS settings look ok?  Also is there a graceful way to test this out other then pulling the plug and waiting a half hour?

Thanks in advance!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

With the UPS set with Low battery at 10 minutes the UPS will send a signal to PCNS when the UPS has 10 minutes of runtime and PCNS will start the VM, Host, and OS shutdown (in that order). The UPS will not power down until the battery is drained. As long as it does not take longer then 10 minutes for the VMs, Host, and OS to power down gracefully everything will be fine. If it takes longer then that amount of time the low battery time frame should be increased.

Here is the description of Maximum Required Delay from the NMC help file

Maximum Required Delay Calculates the delay needed to ensure that each PowerChute client has enough time to shut down safely when the UPS or the PowerChute client initiates a graceful shutdown. Maximum Required Delay is the longest shutdown delay needed by any server listed as a PowerChute Network Shutdown client. This delay is calculated whenever the management interface of the UPS turns on or is reset, or when "Force Negotiation" is selected as Maximum Required Delay. "Force Negotiation" polls each client for information on the time it needs for a graceful shutdown. Two extra minutes to allow for unforeseen circumstances is then added to the calculated time. The negotiation can take up to 10 minutes. If you do not select "Force Negotiation", two minutes is used by default as the shutdown delay for all clients.

What that means is when you add VM, vApp, VCSA, and command files delays the NMC is given that information. The NMC add up all that time and enters it as the Maximum Required Delay so that the UPS knows it need that amount of time to ensure the each PowerChute client is shut down gracefully.

Example: VM shutdown delays of 120, vCenter Server delay of 240 = 6 minutes plus 2 additional non configurable minutes = 8. With those numbers the low battery and maximum required delay should be 10 minutes.

As I wrote earlier if you are going to configure Runtime remaining below threshold I suggest it be greater than Low Battery. Since you need 120 second for the VMs and 240 for vCenter shutdown and are not including VM start up I would set Runtime remaining below threshold to 1080 seconds. 10 minutes for low battery, VM shut down, vCenter shut down, plus 2 minutes = 18 minutes or 1080 seconds. This way the UPS never gets to low battery.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

Hello,

With what you have configured now when the UPS has 10 minutes of battery left (low battery) it will send a signal to PowerChute and VMs / host shut down will start.

If you are looking for descriptions of the event actions you can review the users guide (starting on page 75) or click on the question mark on the PowerChute web page to launch help file.

Here is the description of Runtime remaining below

  • When the UPS is running on battery power and the runtime remaining on the UPS drops below the threshold, PowerChute will trigger a shutdown sequence. 

If you are going to configure Runtime remaining below threshold I suggest it be greater than Low Battery. Since you need 120 second for the VMs and 240 for vCenter I would set Runtime remaining below threshold to 1080 seconds. 10 minutes for low battery, VM shut down, vCenter shut down, plus 2 minutes = 18 minutes or 1080 seconds.

With that setting when the UPS battery fails below 18 minutes PowerChute will start the shut down process.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

0 Likes
0
879
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

Thanks for getting back to me Bill:

So if I understand.  Right now my UPS is going to shutdown at the 10 min power remaining mark.  If I dont adjust the threshold on the PCNS event "Runtime remaining below threshold" there will be no time to shut down theVMs.  On the APC under the PowerChute settings there is:

Maximum Required Delay: 10 minutes

What is that?

I know your not supposed to run the batteries all the down,  so what is a safe number on when to shut it down?

Where is the best place to start the VM shut down?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

0 Likes
0
880
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 12:02 AM . Last Modified: ‎2024-02-29 11:37 PM

With the UPS set with Low battery at 10 minutes the UPS will send a signal to PCNS when the UPS has 10 minutes of runtime and PCNS will start the VM, Host, and OS shutdown (in that order). The UPS will not power down until the battery is drained. As long as it does not take longer then 10 minutes for the VMs, Host, and OS to power down gracefully everything will be fine. If it takes longer then that amount of time the low battery time frame should be increased.

Here is the description of Maximum Required Delay from the NMC help file

Maximum Required Delay Calculates the delay needed to ensure that each PowerChute client has enough time to shut down safely when the UPS or the PowerChute client initiates a graceful shutdown. Maximum Required Delay is the longest shutdown delay needed by any server listed as a PowerChute Network Shutdown client. This delay is calculated whenever the management interface of the UPS turns on or is reset, or when "Force Negotiation" is selected as Maximum Required Delay. "Force Negotiation" polls each client for information on the time it needs for a graceful shutdown. Two extra minutes to allow for unforeseen circumstances is then added to the calculated time. The negotiation can take up to 10 minutes. If you do not select "Force Negotiation", two minutes is used by default as the shutdown delay for all clients.

What that means is when you add VM, vApp, VCSA, and command files delays the NMC is given that information. The NMC add up all that time and enters it as the Maximum Required Delay so that the UPS knows it need that amount of time to ensure the each PowerChute client is shut down gracefully.

Example: VM shutdown delays of 120, vCenter Server delay of 240 = 6 minutes plus 2 additional non configurable minutes = 8. With those numbers the low battery and maximum required delay should be 10 minutes.

As I wrote earlier if you are going to configure Runtime remaining below threshold I suggest it be greater than Low Battery. Since you need 120 second for the VMs and 240 for vCenter shutdown and are not including VM start up I would set Runtime remaining below threshold to 1080 seconds. 10 minutes for low battery, VM shut down, vCenter shut down, plus 2 minutes = 18 minutes or 1080 seconds. This way the UPS never gets to low battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of