Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

AP9630 sporadic reboot and emailing reboot notification code 0x0101

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9630 sporadic reboot and emailing reboot notification code 0x0101
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
9
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

AP9630 sporadic reboot and emailing reboot notification code 0x0101

This was originally posted on APC forums on 3/16/2015


I've got an AP9630 installed in an SMT2200 running 6.2.1 that is sporadically rebooting a few times a week. When it does so, or it is instructed to reboot, it emails out the 3 listed recipients an Informational warning. I have disabled all Informational warnings for email and set them to syslog instead. I have set only Critical notifications to send an email. However, this notification email still goes out every time. Where can I remove the configuration for code 0x0101 to remove it from sending an email?

Code : 0x0101

Informational - UPS: Restored the local network management interface-to-UPS communication.
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • 0x0101
  • reboot
  • sporadic
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This was originally posted on APC forums on 3/16/2015


Whoa. Yeah, add me to the list. I just ran a self test and got the email notification for it as well. That's another one. I definitely want the failure notification, but don't want regular updates that say "I'm still working correctly." At least I can drop that notification down to myself only and not other personnel, but I'd just as soon be rid of it.

What I meant above regarding 0x0101 is that it does not even appear under Power Events -> Communication, and as such cannot be an edited item. The only way to get to it was to manually change the URL as listed in the PDF that you pointed me to. 

See Answer In Context

Reply
Share
Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This reply was originally posted by Angela on APC forums on 3/16/2015


Hi Kevin,

It'd be helpful to see the event.txt, config.ini, and data.txt and maybe I can tell you why it is sporadically rebooting or guide you on that. Instructions are here on getting logs (or the .tar file) -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156131  

To disable any code that is not on the event list, you can read/follow instructions here and use the 0x0101 code where reference -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156104 

Reply
Share
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This was originally posted on APC forums on 3/16/2015


Hi Angela. Note that I'm looking at the 3:22 unscheduled reboot, as well as the 11:40 scheduled reboot. The warnings at 5:32 and 5:42 were successfully logged and not emailed as desired.

Ok, attaching the files is failing in Chrome, Firefox, and IE. Hmm.

Reply
Share
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This was originally posted on APC forums on 3/16/2015


Ok, attaching files fails under linux as well as windows. Wow.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This reply was originally posted by Angela on APC forums on 3/16/2015


Hmm. I use Chrome/Firefox on Windows and I haven't seen a problem with attaching files. Feel free to elaborate on the specific issue and I can have it looked at for attaching files. If you want, send an email with the attachments to upload.Logs_fr.vup7y92eeu@u.box.com which will go to a Schneider Box folder I have set up.

Reply
Share
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
678
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This was originally posted on APC forums on 3/16/2015


Ok, I had to email the box address. I just can't get anything to attach to the forum interface. After clicking the "Show" to open the Attach Files, I click to select files, navigate to my local file directory and select the file. As son as it is opened, I see a progress bar flash by and disappear, like it's uploading the file, but it doesn't give me any progress. It disappears basically immediately. I'm on Chrome right now and have disabled any extensions to verify nothing is interfering. Same thing is seen under IE as well as Pale Moon (rebranded Firefox).

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This reply was originally posted by Angela on APC forums on 3/16/2015


Thanks for the detailed feedback on the attachment issue. I'll look into that as well.

I did get the .tar file in the box folder - thank you.

After the NMC reboots for any reason, it is normal to see anywhere from 3-5 events reported that are standard to show afterwards. For your UPS device, it would be these: 

03/10/2015 11:09:38 Device UPS: The power for switched outlet group 1, Outlet Group 1, is on. 0x0185
03/10/2015 11:09:38 Device UPS: The power for the main outlet group, UPS Outlets, is on. 0x0185
03/10/2015 11:09:38 Device UPS: Restored the local network management interface-to-UPS communication. 0x0101
03/10/2015 11:09:22 System Network service started. IPv6 address FE80::2C0:B7FF:FEB6:D7A4 assigned by link-local autoconfiguration. 0x0007
03/10/2015 11:09:20 System Network service started. System IP is X.X.X.X from manually configured settings. 0x0007
03/10/2015 11:09:14 System Network Interface restarted. 0x0002

Going back to your original question, did what I mentioned about configuring clearing events help you disable this email? You just may have a scenario where not specific to a reboot, NMC to communication won't establish, you fix it, and then it won't tell you that. If you're looking at syslog too, then it sounds like it is not a huge concern.

Now, specific to the sporadic reboots... 

I saw these:

03/15/2015 03:21:23 System Network Interface restarted. and 03/10/2015 09:07:23 System Network Interface restarted. 

debug.txt and dump.txt help us with these. Your dump.txt is what I have seen in the past relating to an issue we are addressing in future revs relating to SSH and a potential memory leak. Sure enough, I thought this and checked your config.ini and I see you use SSH and not telnet.

For this one, I'd say it appears to be the reboot is freeing up the memory and we hopefully will have that addressed in the next future rev. I don't think it is anything you can address on your own besides usng Telnet which is a silly suggestion for a fix tongue-out.

I hope this helps. Let me know if you have further questions.

Reply
Share
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This was originally posted on APC forums on 3/16/2015


Hello again Angela. Following the linked pdf and manually editing the URL to go directly to code 0x0101 did allow me to edit the notification event and remove the emails from notification and set it to syslog only. I did a reboot and the change appears to have been applied, as I have not yet received an email notification. So that problem appears to be solved...

The notification is not listed under Power Events -> Communication though. The only events listed there are for codes 102 and 148. This looks like a bug in the firmware I take it? Or perhaps it was intentionally left out of the 6.2.1 release for some other reason?

Regarding your latter comments: Yes, I use SSH. I can't fathom anyone using telnet these days.. So please ask the programmers to expedite any SSH related programming. 🙂

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This reply was originally posted by Angela on APC forums on 3/16/2015


Hi Kevin,

It is not a bug, it is just how informational events are handled. 0x0102 code is the event you'll see on the list (UPS: Lost the local network management interface-to-UPS communication.) and 0x0101 clears that condition. This just happens to be an event where the "clearing condition" is more frequently active/true versus the "alarm" condition associated with it. Another example is outlined in the kbase that people often feel similarly with - self test failed/passed. Your self test is typically passing and the passed event is the clearing condition for the self test failed alarm which happens, and then is cleared when you address the problem. People don't want to see the self test passed event every two weeks but then if they disable it, and have a self test failed, they won't know when it passes again after addressing it.

Hope that helps clarify!

Reply
Share
BakCompat_apc
Ensign BakCompat_apc
Ensign

Posted: ‎2021-07-08 12:02 AM

0 Likes
0
679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-08 12:02 AM

This was originally posted on APC forums on 3/16/2015


Whoa. Yeah, add me to the list. I just ran a self test and got the email notification for it as well. That's another one. I definitely want the failure notification, but don't want regular updates that say "I'm still working correctly." At least I can drop that notification down to myself only and not other personnel, but I'd just as soon be rid of it.

What I meant above regarding 0x0101 is that it does not even appear under Power Events -> Communication, and as such cannot be an edited item. The only way to get to it was to manually change the URL as listed in the PDF that you pointed me to. 

Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc