Powerchute Network Shutdown not writing to Windows event log

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Network Shutdown not writing to Windows event log
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:01 AM

0 Likes
3
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:01 AM

Powerchute Network Shutdown not writing to Windows event log

We were running PowerChute 2.2.4 and found it wasn't writing events to the WINDOWS event log (Such as one server that wasn't communicating with the UPS, and we weren't aware of it.) We did have all events in the PCNS webpage set to write to the event log, but I assume this is the PCNS log.

In past versions, I know PCNS used to write to the Windows event log. What changed? We upgraded to v3 and it still doesn't write to the Windows event log. Since we can't email from PCNS, and it won't write to the Windows event log, how are we supposed to monitor it?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:00 AM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:00 AM

i am not sure - i was told only powerchute plus, powerchute business edition and powerchute personal edition did this. i wasn't aware PCNS did this at any point in its release history.

within PCNS, when you are setting it up, there is an event that you can configure to log an event (which is enabled by default), notify users (via Messenger service if supported), run a command file, or shut the system down. you can do the same type of configurations if the communication is lost while on battery. this might be something you'd like to configure or perhaps write a command file to do some other type of action in order to notify you. other than that, there isnt really an option that i can see.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:01 AM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:01 AM

PCNS has its own event log and does not do any writing to windows event log. only powerchute personal edition does that.

within PCNS 3.0, if you click on your server name on the navigation pane to the left (after you login), i believe the page defaults to View Event Log.

to get to PCNS 3.0, I think a shortcut is installed on the start menu but if not, use a web browser to go to http://:3052 or I think https://:6547 will work too. this is how you manage and configure PCNS. if the web page doesnt come up, ensure the PCNS service is started within Administrative Tools->Services and also, you might need to add those URLs to your Trusted Sites, especially if this is a server OS like windows server 2003/2008.

hope that helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:01 AM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:01 AM

Yes - understood that PCNS has it's own event log. After a power outage, we were looking at it and wondering why we never received an alert that we weren't communicating with the UPS when all of our other servers were.

The issue is - at one time, PCNS communicated with the Windows event log. We query the event log for certain events, and this is how we normally know if anything is broken. We can't query the PCNS log, so we're stuck. Why would APC take this feature away? Yet another reason to look to another UPS vendor. . .

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:00 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:34 AM . Last Modified: ‎2024-03-06 03:00 AM

i am not sure - i was told only powerchute plus, powerchute business edition and powerchute personal edition did this. i wasn't aware PCNS did this at any point in its release history.

within PCNS, when you are setting it up, there is an event that you can configure to log an event (which is enabled by default), notify users (via Messenger service if supported), run a command file, or shut the system down. you can do the same type of configurations if the communication is lost while on battery. this might be something you'd like to configure or perhaps write a command file to do some other type of action in order to notify you. other than that, there isnt really an option that i can see.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore