Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner

Powerchute Network Shutdown Utility

APC UPS Data Center & Enterprise Solutions Forum

Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Network Shutdown Utility
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5022
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
15
1210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

Powerchute Network Shutdown Utility

This was originally posted on APC forums on 8/10/2012


I just set up a SMX1500RM2UNC. It comes with the network card AP9631.

Is there a version of the network shutdown utility that works with Windows 7 x32? I was not able to find one.

thanks,

Mike

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:28 AM

0 Likes
0
1208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:28 AM

This was originally posted on APC forums on 8/28/2012


i picKed a winna and voidstar thansk.

I changed the Power Off Delay under Sequencing to 7 minutes.

Under load shedding, I unchecked the "Skip Outlet Off Delay." I assume if I leave this checked then the above change to 7 means nothing.

Also, under sequencing, I changed "Power On Delay" to 5 minutes. I assume this means that power must be restored to the UPS for 5 minutes before the outlet turns on.

Here is a screen shot.

Please let me know if this is correct.

thanks.

Message was edited by: rinconmike

See Answer In Context

Attachments
Reply
Share
Replies 15
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/29/2012


Out of curiosity, Voidstar noted:

"You could also increase the "script execution time" in PCNS. Then, PCNS will automatically increase the power off delay if it's too short."

I am not running a specific script. I Just checked the box to shut down system under Configure Events / UPS: On Battery.

Is there a place to enter/increase script time?

I think what i have by doing it on the UPS works (I still need to pull the UPS plug and test), but curious about this other method.

Is one better than the other?

thanks,

Mike

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This reply was originally posted by Angela on APC forums on 8/30/2012


its just another delay you can impose without actually running a script. the management card will know that a script delay is there and increase the delay as opposed to what I had instructed you to do. it would work either way - to me if you are not using a script and don't want to be confused later when you go back or someone else does and wonders why the delay is set with no running script, i'd do it my way.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This reply was originally posted by Angela on APC forums on 8/14/2012


yes, powerchute network shutdown 3.0.1 should work fine. my understanding is even though it should work fine, its not officially tested because powerchute network shutdown is not designed for workstation OSs - more server class. i think this might change down the line.

just install the 32 bit version listed under windows server 2003 or 2008.

Reply
Share
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/15/2012


thanks. is there any benefit of using powechute business 9 instead? It looks like I can do all the configuration of the UPS through the network card so business edition is not really needed.

thanks,

Mike

Message was edited by: rinconmike

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This reply was originally posted by Angela on APC forums on 8/15/2012


no. i would just use the network management card and its more powerful in a few respects than powerchute business edition. powerchute network shutdown is for the graceful shutdown of your operating system and computer thats attached to the UPS. if you don't need that, powerchute network shutdown is not required.

Reply
Share
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/15/2012


ok. thanks. I installed the network shutdown utility on the pc and used the wizard to configure.

I am not sure how it works now. I have the pc hooked to outlet group 1. I want to be able to shut down the pc and outlet group 1 when there is 30 minutes of battery time remaining. I know how to use the web ui to shut down the outlet when there is 30 min remaining (under UPS/Configuration/Outlet Groups/Group 1/ then select Turn Off Outlet Group when: UPS runtime remaining is less than xx seconds.

How do I set the PC to shutdown first using the network shutdown utility?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This reply was originally posted by Angela on APC forums on 8/15/2012


i checked on this. FYI, i started with http://www.apcmedia.com/salestools/PMAR-8RNKEY_R0_EN.pdf

what you'll need to do is you should have an option or had an option in the configuration wizard to select the outlet group and tell PCNS that your computer is connected to outlet group 1. then what you need to do is have that option you mentioned in the NMC configured to turn that outlet group based on the conditions you specify.

the last thing I'd do is then decide what you want to do in regards to the UPS shutting off after that PCNS client turns off. that was under Miscellaneous in the configuration wizard.

You can select the Turn off Power Source when PCNS shuts down the server field if you want the actual UPS to turn off when the PCNS server shuts down. (This does not apply to certain UPS devices: Parallel Silcon and Parallel-UPS configurations, Smart-UPS VT or Galaxy UPS devices).+

then, check PDF page 41 on http://www.apcmedia.com/salestools/PMAR-8P9G2C_R2_EN.pdf which goes over how the shutdown will work on a UPS with outlet groups.

hope that helps.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This reply was originally posted by Angela on APC forums on 8/16/2012


i also found this: http://nam-en.apc.com/app/answers/detail/a_id/11372

Reply
Share
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/16/2012


thanks. it is really not clear how it works. I think I need to play with it and just test it.

If I program an outlet group on the UPS to turn off when there is 20 min of run time left, will it send an alert to the Workstation to shut down and then delay the outlet shutoff for a set time? That is what i want it to do. Or do I need to program that in the shutdown utility and after shut down tell it to turn the outlet group off.

Then I would want the outlet to come back on when there is 45 min of run time left. The bios of my computer is set for when power is restored, boot the computer show with power restored to the outlet group, the computer should turn on.

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This reply was originally posted by Angela on APC forums on 8/29/2012


yes, that appears correct. I'd give it a go.

Reply
Share
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/28/2012


>
is it the power off delay under sequencing I need to increase? maybe double to 240?
>

You could do that. You could also increase the "script execution time" in PCNS. Then, PCNS will automatically increase the power off delay if it's too short.

>
Last question, is there a setting somewhere that requires the power restored to the UPS to me on for 5 minutes before the outlet group power is restored? I just do not want it to be restored for a minute, turning the outlet group on and then having another power outage causing everything to turn off again.
>

That's the "min return runtime" setting.

Reply
Share
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/27/2012


in the PCNS Web UI, I went in under configured events and clicked on "Shut Down System" for "UPS: On Battery."

I then made it for 600 seconds (10 minutes).

Under "Configure Shutdown" I did not fill in "Run this command file (full name):" or " The command file needs this much time to complete (seconds):"

I did select "Turn off this servers Outlet Group at the UPS after the shutdown finishes." which should turn the outlet group off after the computer shuts down.

Does that sound right to have it shut down 10 minutes after on battery?

Now for automatic restart, I do have my PC bios set to turn on when power restored.

So with the shutdown the way I have it set, the Outlet group should also be turned off on the UPS after the PC shuts down. So when the power is restored to the UPS, will the outlet group turn back on restoring power to the PC?

Also, on the UPS Web UI, under configuration, under outlet groups for the pc outlet, I left the defaults. which are:

Sequencing
Power Off Delay: 120 seconds
Reboot Duration: 8 seconds
Power On Delay: 0
Min Return Runtime: 0

Under Load shedding, the only item checked is "Skip outlet off delay."

Last question, is there a setting somewhere that requires the power restored to the UPS to me on for 5 minutes before the outlet group power is restored? I just do not want it to be restored for a minute, turning the outlet group on and then having another power outage causing everything to turn off again.

thanks,

Mike

Reply
Share
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:27 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:27 AM

This was originally posted on APC forums on 8/27/2012


i tried it. however, the outlet group turned off too soon. The system was not fully shut down yet.

is it the power off delay under sequencing I need to increase? maybe double to 240?

Reply
Share
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:28 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:28 AM

This reply was originally posted by Angela on APC forums on 8/28/2012


sorry for the delay. i asked someone for assistance and they did some testing.

Configure the on battery event to shut down the OS after being on battery for 10 minutes. You have already done that. After being on battery for 10 minutes PCNS will command the OS to shutdown and send a shutdown signal to the UPS to power off the outlet group. This has been done also. We need you to configure the delay for the outlet group (according to your post, the delay is disabled) to be sure the outlet group is not powered off before the OS has a chance to shut completely down killing power to the computer. If the OS takes 5 minutes to shut down he should configure the outlet group off delay of 7 minutes. Adding 2 minutes just to be safe.

The OS will then shut down after being on battery for 10 minutes and the outlet group will power down 7 minutes later.

i hope that helps. this was the feedback I got.

Reply
Share
rinconmike_apc
Lieutenant JG rinconmike_apc
Lieutenant JG

Posted: ‎2021-07-01 01:28 AM

0 Likes
0
1209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2021-07-01 01:28 AM

This was originally posted on APC forums on 8/28/2012


i picKed a winna and voidstar thansk.

I changed the Power Off Delay under Sequencing to 7 minutes.

Under load shedding, I unchecked the "Skip Outlet Off Delay." I assume if I leave this checked then the above change to 7 means nothing.

Also, under sequencing, I changed "Power On Delay" to 5 minutes. I assume this means that power must be restored to the UPS for 5 minutes before the outlet turns on.

Here is a screen shot.

Please let me know if this is correct.

thanks.

Message was edited by: rinconmike

Attachments
Reply
Share
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc