Powerchute Network Shutdown 4.4.3 Virtual Appliance - Refusing connection to web interface
Hi,
I have just installed PCNS 4.4.3 Virtual Appliance on a VMWare ESXi 6.0 host. I configured the initial settings via the console and restarted. I can ping the PCNS VA IP address but cannot connect to the web interface https://Server IP:6547 to continue configuration.
I am on the same subnet with no firewall in between and when using windows network troubleshooter it reported that the server is running but refused my connection.
I had the same issue with PCNS 4.4.2 and upgraded to 4.4.3 hoping that it was just an issue with the version.
I also have other servers running PCNS 4.4.1 without issue.
Any help would be appreciated.
Thanks
- Labels:
-
Business Power Software & NMC
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-26 05:29 AM
You need to set the web UI username and password. See Schneider Electric FAQ PowerChute Network Shutdown version 4.4.2 & 4.4.3 web page is not accessible after installing onto s...
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-26 01:08 AM
hello,
Also having the same issues. After install Powerchute Network Shutdown 4.4.3 Virtual Appliance. The server boots and I see the ip of the server with port 6547 to continue the setup. But I am getting an error. Website can not be contacted.
Can someone please assist with this issue.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-26 05:29 AM
You need to set the web UI username and password. See Schneider Electric FAQ PowerChute Network Shutdown version 4.4.2 & 4.4.3 web page is not accessible after installing onto s...
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-07-26 10:11 AM
Thanks, this worked. The change in default behavior had me perplexed.
Much appreciated!
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-24 03:30 PM
It's still did not work. I restarted the services but still can't access/config the server.
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-24 03:42 PM
Can you tell us what comes up if you use the systemctl status PowerChute command?
Will you be able to check as well if the ports mentioned in the FAQ article below are open on your network/software firewall?
What ports are utilized by PowerChute Network Shutdown and how are they secured?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-24 08:08 AM
hi , just found the same problem on my upsva pcns vmware 4.4.2 , no more access via https gui
link provided do not work anymore but on internet i have found to check systemctl status...my PowerChute was not present so i do a sudo systemctl enable PowerChute and then sudo systemctl start Powerchute
in this way service is up and running but again no access to the gui.
i have found another post where i need to make a backup copy of the ini file and then add username and password again in a specific section but again restarting the vm no access to the https and checking again the ini file , username and password still there...i read that these credential for security are deleted after setup is completed.
i don't know what to do , this problem happens for an uknown reason after some years of use.
please let me know
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 12:22 AM
Hi , i came across the same problem , i try the link but goes to a 404 page , then i tried to search on internet and found other article that says to use this command: sudo systemctl enable PowerChute and then sudo systemctl start PowerChute but i have not luck
then i found another article that say to add in the [NetworkmanagementCard] username = and password = to do the reconfig but with no luck
that article say also that username and password will be deleted after a restart of the vm for security reason but are still present.
i'm stuck on what to do to solve the problem that appear with no reason because i use this vm for at least 4 years.
please let me know.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 04:19 AM
If you log into the PowerChute VM as the root user you do not need to enter sudo before the commands. What is the status of the PowerChute service? Run the command systemctl status PowerChtue. Is the status running or stopped?
Another question, when you installed the PowerChute VM did you install it through vCenter Server or directly onto the ESXi host? If you installed directly onto the ESXi host see Schneider Electric FAQ000261450
"How to remove the message “PowerChute Services are disabled due to invalid credentials.” on the PowerChute VM."
You should also review Schneider Electric FAQ000266949 "Using the unlicensed version of PowerChute Network Shutdown 5.1 to protect a Standalone ESXi host." Assuming you are not utilizing vCenter Server.
And you should review Schneider Electric FA159758 "How to reset the PowerChute Network Shutdown password and username."
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 06:06 AM
First of all just to mention this vm was installed in 2019 and redo from skratch in 2023 for an upgrade and up to now i was able to login into https gui.
If i sent the systemctl i see this
when yesterday i sent the above command i see an error that says it is not a registered service.....very strange so i sent systemctl enable PowerChute and then systemctl start Powerchute
we install it through vcenter server
i read the FAQ provided but these are not my case because i'm not able at all to see the https gui....when i open firefox or chrome and type https://192.168.10.146:6547 or https://192.168.10.146:6547/login but i get this:
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 07:49 AM
If i login into the vm and i run systemctl status PowerChute i got this:
powerchute vm was installed through vcenter server appliance
i read the FAQ provided but is not my case because this was built in 2019 and in 2023 was rebuild from skratch for upgrade and the access to the https GUI it works up to now.
if i try to open the web gui with firefox or chrome i get this:
maybe the webserver is not working ? but i don't know how to check it
i don't know what else to check...
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 08:02 AM
hi , if i log into the vm and send that command i see that is up and running.
i read the FAQ provided but these are not my case , this vm was installed with vcenter server appliance in 2019 and in 2023 was rebuild from scratch to upgrade to 4.4.2 and i was able up to know to access the https GUI
what can i check ? how can i check if the webserver is down ? maybe could be a problem of the ssl certificate contained in the vm ?
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-25 11:48 PM
if i send the systemctl command it says that it is running
we have install through vcenter server
i have read the FAQ provided but these are not my case.
how can i check if webserver is down or have a problem? how can i check if the ssl cert has a problem?
please let me know
thank's
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-28 12:27 AM
please read my post and reply.
thank's
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 01:31 AM
Any news please?