Hello everybody,
i have a issue with this environment:
We tested the envinroment bypassing the power plug, and this are the events:
02/16/2018 | 16:51:41 | Running Shutdown Command File. |
02/16/2018 | 16:51:10 | vCenter Server is accessible. PowerChute will be able to issue commands to Virtual Machines or Hosts. |
02/16/2018 | 16:51:10 | UPS critical event: On Battery resolved on Hosts esxi03.dominio.nomination.com, esxi01.dominio.nomination.com, esxi02.dominio.nomination.com, 10.64.1.201, esxi04.dominio.nomination.com. |
02/16/2018 | 16:51:00 | Cannot connect to vCenter Server. PowerChute may not be able to issue commands to Virtual Machines or Hosts. |
02/16/2018 | 16:43:50 | SNMPV1: New connection by user public from 10.64.1.222 |
02/16/2018 | 16:24:03 | UPS is no longer running on battery power or output power has been turned on. |
02/16/2018 | 16:19:51 | Shutting down VMs on Host esxi02.dominio.nomination.com. |
02/16/2018 | 16:19:51 | Starting Maintenance Mode Task on Host esxi02.dominio.nomination.com. |
02/16/2018 | 16:19:51 | Shutting down VMs on Host esxi01.dominio.nomination.com. |
02/16/2018 | 16:19:51 | Starting Maintenance Mode Task on Host esxi01.dominio.nomination.com. |
02/16/2018 | 16:19:51 | Shutting down VMs on Host esxi03.dominio.nomination.com. |
02/16/2018 | 16:19:51 | Starting Maintenance Mode Task on Host esxi03.dominio.nomination.com. |
02/16/2018 | 16:19:50 | Shutdown sequence started on Hosts esxi03.dominio.nomination.com, esxi01.dominio.nomination.com, esxi02.dominio.nomination.com, 10.64.1.201, esxi04.dominio.nomination.com in response to UPS critical event: On Battery. |
02/16/2018 | 16:19:50 | UPS critical event: On Battery. |
02/16/2018 | 16:18:50 | UPS has switched to battery power. |
the result was that the nodes went in maintenance but only few vms shutted down.
im going to attach the some logs catched from /opt/APC/PowerChute/group1.
I don't have any dns related issues. Please help me!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:12 AM . Last Modified: 2024-03-11 04:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:11 AM . Last Modified: 2024-03-11 04:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:11 AM . Last Modified: 2024-03-11 04:18 AM
no one can help me?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:11 AM . Last Modified: 2024-03-11 04:18 AM
Hi,
All of the errors below were logged in error.log The errors" findByIP" and "NoPermission or InvalidLogin" are all listed in the troubleshooting section of PCNS VMware User's Guide.
To correct the error "NoPermission or InvalidLogin" you need to create a local account on vCenter Server and each host for PowerChute to use to communicate the shutdown command. See page 19 of Application Note 180.
I also recommend adding the hosts IP addresses and domain names to the /etc/hosts on the appliance to resolve the findByIP errors.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:11 AM . Last Modified: 2024-03-11 04:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:11 AM . Last Modified: 2024-03-11 04:18 AM
thank you for reply, one more question.
The user i have to add to hosts must be pcnsadmin with pcnsadmin as password? is it customizable? if not, i think is a security concern
please let me know
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:12 AM . Last Modified: 2024-03-11 04:18 AM
Hi,
The user name used to log into PowerChute must match the assigned user name PowerChute will use to communicate with the network management card. The password used to log into PowerChute is unique to PowerChute.
The user name and password Powerchute uses to communicate with vCenter Server should be the same user name and password PowerChute would use to log into the individual hosts. The reason is, if PowerChute cannot communicate with vCenter Server it requires the ability to log into the individual hosts to power them down.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:12 AM . Last Modified: 2024-03-11 04:18 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:12 AM . Last Modified: 2024-03-11 04:18 AM
ok, so if im connecting to vcenter using the user upsadmin (just for example) i need to create the same user (with the same password) on all my hosts esxi. is that correct?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:12 AM . Last Modified: 2024-03-11 04:18 AM
Hi,
Yes, that is the recommended configuration.