Powerchute Business Edition can't disover APC device via USB

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute Business Edition can't disover APC device via USB
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
7
1503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

Powerchute Business Edition can't disover APC device via USB

I have two SBS 2003 servers each with a different APC device connected via USB. I installed Powerchute Business Edition Basic on each server without a hitch. This was only about a year ago. Since then the PBE agent service won't start, and PBE doesn't "see" the USB attached APC device. When I tell it to search, it only wants to find a device with an IP address. Both devices are connected via USB. I guess the question is, why won't the agent start? Why can't PBE "see" the USB device? Thanks!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

Powerchute personal edition is the software you are supposed to use so I would recommend that you use that and uninstall business edition. powerchute business edition only works with a 940-0128D cable (RJ-45 to DB9) which only provides simple signaling anyway (which means you will only know if the UPS is online or on battery). no other information you see in PCPE will be shown - like input voltage, etc

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

i picKed a winna wrote:
it sounds like you are using the Business Edition console.

i would try closing that console out, and working with just the PCBE agent. to do that, access the agent via http://127.0.0.1:3052 or http://:3052 in the web browser- this is direct access to the agent.

lets see what you get when you access that. i'd want to know what you are seeing for the UPS status as well as the information under Protected System->System Settings->Communication type.

your interface should look similar to this screenshot (except yours should say USB) i have attached when you access this web agent interface
I have similar problem. I cannot access Protected System->System Settings->Communication type. This option doesn't work for me (page is empty).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

have you tried a different browser? add the IP as well as loopback address to your trusted sites. that may help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

I tried this, but it doesn't work. IE can't find the web page. Probably because the agent isn't running. When I try to start the agent I get:

The APC PBE Agent service terminated with service-specific error 0 (0x0).

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

can you take a screenshot of this error? have you tried to start the service in safe mode? can you show us what the properties box looks like for the APC PBE Agent service, for each of the tabs?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

it sounds like you are using the Business Edition console.

i would try closing that console out, and working with just the PCBE agent. to do that, access the agent via http://127.0.0.1:3052 or http://:3052 in the web browser- this is direct access to the agent.

lets see what you get when you access that. i'd want to know what you are seeing for the UPS status as well as the information under Protected System->System Settings->Communication type.

your interface should look similar to this screenshot (except yours should say USB) i have attached when you access this web agent interface

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1502
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

Hi,

sitting with a similar issue. PCBE Agent starts up but doesn't detect my UPS(Back-UPS 1000 RS) via USB. UPS is detected fine with PC Personal Edition. Is my UPS not compatible, or is PCBE only for Servers(I run XP Pro SP 3 - all updates installed)

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1503
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

Powerchute personal edition is the software you are supposed to use so I would recommend that you use that and uninstall business edition. powerchute business edition only works with a 940-0128D cable (RJ-45 to DB9) which only provides simple signaling anyway (which means you will only know if the UPS is online or on battery). no other information you see in PCPE will be shown - like input voltage, etc

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore