Dear APC technical team,
I have a question about the folowing UPS:
SU2200RMI3U
SU3000RMI3U
SU5000RTXL
SUA3000RMI2U
SURT3000XLI
do they support UPS MIB (RFC 1628) or do they have their standard mibs?
which RS232 protocols do they have,do they work with your custum protocols or not?
Thanks and regards
Arie
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:22 AM . Last Modified: 2024-03-07 03:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:22 AM . Last Modified: 2024-03-07 03:15 AM
Many thanks to your quick response
Arie
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:22 AM . Last Modified: 2024-03-07 03:15 AM
Hello:
Per the following knowledge base, we do not currently support the RFC1628 MIB.
http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7014&p_created=1106841671&p...
We do have our own MIB which is the same file for all of our SNMP supported devices. Our latest version of our MIB (3.95) can be found in the Software & Firmware section or at the following FTP link:
ftp://ftp.apc.com/apc/public/software/pnetmib/mib/395/powernet395.mib
All of the UPS's you mentioned do support our proprietary UPS Link Language through serial. We do also offer a Building Management Card in case you are interested in using the MODBUS protocol. Details found here:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9622&tab=documentation
Let us know if you have anymore questions!
Thanks
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:22 AM . Last Modified: 2024-03-07 03:15 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 08:22 AM . Last Modified: 2024-03-07 03:15 AM
Many thanks to your quick response
Arie