NMC AP9617

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC AP9617
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
5
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

NMC AP9617

Has anybody else had any problems having configuring the AP9619 network management card - i have installed the APC Device IP configuration Wizard which recognises that there is an unconfigured card, i assign ip, subnet and default GW to the card and attempt to browse to the device. this fails everytime. If i run the APC network shutdown software, it too doesn't recognise that there is a network card that has has an address assigned to it.

if i run the config wizard again it will not find the netowrk card - i have to reset using the microswitch on the back of the card.

when i have attempted to config the card using the serial port, or hyperterm onto the card i receive nothing...

I have a rack mounted smart-UPS

p.s. i have installed 2 of these cards into similar UPS and always had issues with the wizard, it detects an unconfigured card, I assign IP, SN and GW but i am unable to browse to the device. The previous 2 configurations have eventually worked, i can't remember what i did to get the wizard, the network management card and the UPS configured correctly.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

yes i am using those port setting, yes i have pressed enter a number of times and i used the cable that came with the UPS...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM


Hi BMF



I've once encountered the similar issue as you did but I was at least able to communicate via serial.


what I did:



- Configure a basic subnet for PC. IP: 192.168.1.1 Subnet: 255.255.255.0
- Use IP Config Wizard to discover and configure an ip of same subnet (eg. 192.168.1.100)
- Login to NMC via HTTP and then change to your prefered IP.



I still prefer using serial. If you have complication with serial make sure no application is loking up your com port (eg. PowerChute)

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

I've hard reset the NMC using the microswitch, i then connected using hyper terminal, configuration was simple. i'd wanted to avoid doing this as it mean't attending site rather than completing config remotely

don't think i'll be using the wizard in a hurry...

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

thing that confuses me is that 3 out of 3 network cards i've installed have all had similar issues, IP configuration wizard only appears to do half a job?!

the previous 2 cards i've installed i've managed to fudge it using just the wizard and the network shutdown software, unfortunately on this occasion i can't get the NMC configured and also seem to be unable to connect using the serial connection...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1457
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

Hi:

What port settings are you using within HyperTerminal? Also what cable are you using?

You should be using either the 940-0024 or 940-1524 cables, and using port settings 2400/8/n/1/n. Once you've done this and connected through HyperTerminal, hit enter a few times and you should get a Username prompt. Here you can enter in the username of apc and password of apc and you should be able to access the card and change your network settings from there.

Let us know if you have trouble!

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
1458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

yes i am using those port setting, yes i have pressed enter a number of times and i used the cable that came with the UPS...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore