PCNS not talking to UPSs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS not talking to UPSs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
10
5861
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:22 AM . Last Modified: ‎2024-03-07 03:15 AM

PCNS not talking to UPSs

Hi,

I have two UPS's at the moment that I have got MNCs for. They are Smart-UPS 3000's. I have installed the PCNS software on one test server and have been trying to get it to shutdown when I pull the power out of one of the UPSs. However, the management station will not communicate with the Management Cards.

I can ping the cards from the server and I can telnet to the server on port 3052 form another pc. I can't think what else could be causing the issue. Any ideas?

Oh, there is no firewall turned on on the server which is running Server 2003 Std.

Thanks for any help.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network_management_card
  • PowerChute
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

From looking at one of your wireshark captures, it looks like you may have an incorrect subnet mask configured on the card. The broadcast is being sent to 192.255.255.255 which is indicative of Class A mask. Looking at the rest of your IP addressing scheme, it seems you have a 255.255.0.0 mask. Can you verify if the mask is correct on the cards?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:15 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:15 AM

you definitely want to make sure that ports 80 and 3052 as well as 6547 (if using PCNS v 2.2.3) are open for TCP and UDP as well as incoming and outgoing connections. I realize you said you didnt have a firewall turned on but i have run into issues where firewall rules still get pushed out under group policy. also, you want to make sure the admin user name and password of the NMC is the same as what you are putting for the PCNS installations.

are the PCNS clients timing out when you are installing where they arent registering? (at the end of the installation, PCNS goes out and tries to register with the PCNS client and will tell you that registration is successful or not) or is it installing successfully and registering, then you are accessing PCNS and it says in the event log Powerchute cannot communicate with the network management card?

do you have a screenshot of the error you are getting as well just to confirm?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

Hi,

Sorry for the delay in getting back to you. I have tried connecting to the NMC and server via telnet on the ports specified and I am able to make a connection so something is at least listening. I have attached screenshots of various bits and pieces for you to see exactly what I mean.

I have tried installing the latest firmware on one UPS but this seems to make no difference. I downloaded the latest pcns 2.2.3? but this would not install, it gave a timeout when trying to talk to the UPSs.

Any further ideas?


Thanks,

Chris

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

hi chris. since the PCNS client is registering successfully, it makes me think there is something going on with UDP port 3052 (incoming and outgoing). if you can guarantee the port is open by some method, then the only other things that would be happening are that someone is changing the authentication phrase either on the NMC or on the PCNS side, or the administrator user name has been changed. it needs to be the same on the card and PCNS installation.

dual network cards may also cause an issue like this. you could try changing your binding order if this is a setup you have. PCNS uses the first NMC in the binding order. This is under Network Connections->Advanced Menu at the top of the window->Advanced Settings->Adapters and Bindings.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

Hi,

We do have our servers connected with two NICs in a team. Only the team i/f has any bindings for TCP/IP so this is the only interface that will be used.

I know that I can set the port that is used by the NMC, is it possible to change the port used by PCNS? Perhaps something else has grabbed 3052 although the server shows as listening on that port (*:* for UDP) in a netstat.

I'm sure the auth strings are correct as I have reset them, should I reboot the NMC after doing this or would it take the updated details whilst it is running?

Cheers,

Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

i believe it should update automatically. you can log back out and log back in to make sure changes take effect. if the card needs to reboot, it will when you log out. you can change the port that PCNS runs on but it isnt recommended. [the method is mentioned in this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=651]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

Also, just to be sure the cards in the UPS have a default gateway configured? This is a requirement.

If changing the subnet and re-installing PCNS 223 did not fix I am leaning towards the NIC teaming configuration. Obviously, the easiest way to determine this would be to remove the teaming setup and attempt this installation with one NIC. You would know within 2 minutes if communication were to fail. I don't know the consequences of you breaking the team (reboot required? server downtime etc) so I am not sure how feasible this option is for you. Either way, I assume you'd want this to work with the teaming setup to keep your redundancy or whatever your reasoning for the teaming. Can you provide more information about this teaming setup to possibly determine if there are any changes that can be made?

Message was edited by: Grenade

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

Hi,

I have run a network trace (see attached for results image).

I noticed there was an issue with the NetBIOS name query (even though it is using the correct IP addresses) so I tried adding the UPS's host name into the servers hosts file. This stopped this error from occuring (see second trace image). This has caused a change in the event logs output in PCNS (see image) as the app is resolving the IP to the hostname (some is blurred out). I have not changed or added the second UPS to the host file. I have also tried adding entries to the lmhosts file but this has not helped in any way.

Does this offer any light into what is going on?

Thanks,

Chris

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

Hi,

You are quite correct.

Have made the changes to the NMCs but no difference to result. Have uninstalled the app and removed the server ip as a client on the UPSs, then reinstalled. All appears to be ok install-wise but I'm still getting the same results in the PCNS event log.

Thanks,

Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5858
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

Hi,

Sorry for the dealy in getting back.

Well, I started again from scratch, removed the software, re-entered the config on the NMCs and guess what, all is working as you would expect.

I have no idea what was wrong but I guess I had not put some detail in incorrectly somewhere.

Sorry for the fuss and thanks for all your help.


Chris

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

0 Likes
0
5859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:23 AM . Last Modified: ‎2024-03-07 03:14 AM

From looking at one of your wireshark captures, it looks like you may have an incorrect subnet mask configured on the card. The broadcast is being sent to 192.255.255.255 which is indicative of Class A mask. Looking at the rest of your IP addressing scheme, it seems you have a 255.255.0.0 mask. Can you verify if the mask is correct on the cards?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore