Powerchute BE can't find SMT750 via USB.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Powerchute BE can't find SMT750 via USB.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

0 Likes
4
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

Powerchute BE can't find SMT750 via USB.

Hello all,

I'm attempting to install PowerChute BE on a Windows 10 Pro workstation(version 1703, AKA Creators Update) with a SMT750 hooked up to it via USB cable, but PowerChute simply can't find the UPS. Windows does see the UPS, and lists it in Device Manager as both an "APC UPS" in the Batteries section and as "American Power Conversion USB UPS" in the Human Interface Devices section.

R5h1i6m5j8yChHwWnroWTg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngR5h1i6m5j8yChHwWnroWTg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

The APC USBTerm.exe program that has been linked to on the forums here also sees the UPS. It successfully pulls the model, firmware versions and serial number for the UPS.

yWhWq9P3hO32Bwgat6ZuzQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.pngyWhWq9P3hO32Bwgat6ZuzQ%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png

I've tried both PowerChute BE v9.1.1 and v9.2.1.

Any ideas? frown

Thanks,

MP

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

Hi,

Select RJ45 and then proceed with the installation. Selecting RJ45 tells PowerChute that the UPS is a SMT. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

Hi,

Sorry for the inconvenience. Is PowerChute failing to install or once installed is it reporting that it cannot communicate with the UPS?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

0 Likes
0
2147
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

Hi, thanks for helping.

The Powerchute Agent does install, it just doesn't find the UPS during or after setup. The first screen in the setup wizard says it can't find the UPS automatically, and prompts me for the connection type.

mk1DPkAmyqq6sxaZIEg%2Bkg%3D%3D.pngmk1DPkAmyqq6sxaZIEg%2Bkg%3D%3D.png

I just leave it at DB9 and hit OK. A little later in the setup wizard I get the option to define what the UPS is, so I fill in Smart-UPS and USB.

e49s1JlYLvfhGc7cyBGM9A%3D%3D.pnge49s1JlYLvfhGc7cyBGM9A%3D%3D.png

Installation completes, but when logging into the agent it can't establish a connection.

1IK2x2gYIgR2geMv%2FTZYSQ%3D%3D.png1IK2x2gYIgR2geMv%2FTZYSQ%3D%3D.png

Should I be using different settings?

Thanks,

MP

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

0 Likes
0
2148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

Hi,

Select RJ45 and then proceed with the installation. Selecting RJ45 tells PowerChute that the UPS is a SMT. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

0 Likes
0
2148
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 10:43 PM . Last Modified: ‎2024-03-12 01:11 AM

Oh, wow. You're absolutely right, that's fixed it. Thanks Bill! smile

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore