Posted: 2022-03-28 09:04 AM
PowerChute only shutting down 1 host
We have 2 servers running ESXi.
1 server is plugged into Outlet group 1 and the other server is plugged into Outlet group 2.
We are using vCenter with a vSphere cluster. I have installed PowerChute on ESXi server 1. I have tried to setup PC as a single UPS and advanced to add both hosts to the outlet groups. My problem is is both configurations only ESXi server 1 actually shuts off. Shouldn't both servers shut off? I am sure I am missing something. Please let me know if you need more configuration info.
Thanks!
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-03-31 03:26 PM
You only need to install PCNS on one of the ESXi host and configure for vCenter. Then add both host to the protect host list.
You also need to created a user a user that will be used by PCNS to communicate with the hosts and vCenter See Schneider Electric FAQ FA413356
I also recommend you review Application Note 180 and PCNS VMware User's Guide.