PowerChute does not allow enough time to shutdown all VMs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute does not allow enough time to shutdown all VMs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:02 AM

0 Likes
8
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:02 AM

PowerChute does not allow enough time to shutdown all VMs

Hello,

I am able to shutdown one ESX cluster(test with only 3 VMs) using PowerChute 3.0 with no problems.
My issue is when I try to shut down a second cluster it does now allow enough time to shut down all the VMs on it. It seems the ESXi host has a two minute uptime after it receives the shutdown command. The cluster has 20 VMs, but it only gets to shutdown 3 VMs before the ESXi host finally shuts down.

I have played with changinig the order of the ESXi hosts on the vMA box, but I can only consitently shutdown my first cluster.

The cluster has two ESXi host running version 5.0.

Any help is appreciated.

Thanks.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

See the following Kbase:

http://nam-en.apc.com/app/answers/detail/a_id/11622/kw/HA

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:02 AM

0 Likes
0
1620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:02 AM

Try adding time to the "Command File Execution Duration". That should give your VMs a longer time before the UPS shuts down.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

Thanks for your reply.

Do I have to define a command file to run? Event though I do not need one? It does not let me save any changes to 'The command file needs this much time to complete (seconds): ".

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

I added 600 seconds to the "The command file needs this much time to complete (seconds)" along with an empty command file. All it did was delay the shutdown of the ESXi host for another 10 minutes, but the host still turned off before shutting down all the VMs.

What am I missing?

This is PowerChute Network Shutdown version 3.0.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

Good day Powerchute Guy,

I hope this helps. [Configure PowerChute Network Shutdown to shutdown virtual machines on VMware ESX and ESXi|http://nam-en.apc.com/app/answers/detail/a_id/10380]

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

Thanks for the reply Kulot, but I have read and configured those settings.

To summarize:
-The ESXi host does receive the shutdown command.
-The VMs start to shutdown, but it only gets to successfully shutdown 3VMs (total of 20) before the ESXi host turns OFF.
-It seems that the ESXi host only has about 2 minutes of up time after it receives the shutdown command..
-The VMs do not have enough time to shutdown before the ESXi host turns OFF.

Is there must be a setting I am missing.

Message was edited by: powerchute_guy

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

Do the VMware Tools need to be current?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1619
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

Oooooooooooooops!

All I had to do was increase the "Shutdown Delay" time from 20 seconds to 480 seconds! I should take breaks more often.

Thanks to everyone that responded.

Now on the my second problem. How to shutdown the cluster without having High Availability vMotioning all VMs from one host to the other while PowerChute trys to shut them both down. =(

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

0 Likes
0
1620
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:08 AM . Last Modified: ‎2024-03-06 02:01 AM

See the following Kbase:

http://nam-en.apc.com/app/answers/detail/a_id/11622/kw/HA

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore