PowerChute Network - Wrong Passphrase

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network - Wrong Passphrase
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
8
6335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:37 AM

PowerChute Network - Wrong Passphrase

I'm getting this error on my Communicatin Settings "The security details provided do not match the settings on NMC(s): xxx.xxx.xxx.xxx"
 
My Hardware:
APC Network Management Card 2 9630
Smart-UPS XL 3000 RM 3U 230V (SUA3000RMXLI3U)
 
My Troubleshooting steps so far:

I log into my NMC and reset the pass phrase under
PowerChute > Configuration
Reinstalled the powerchute Network software - no change
upgraded to 4.3.0 - no change
I looked at this post
https://community.se.com/t5/APC-UPS-Data-Center-Enterprise/Cannot-connect-to-UPS-NMC-from-Powerchute...
But I don't have an Administration tab on my NMC web interface
Then I thought maybe I need to update the firmware to make that tab menu available.
I've downloaded the latest firmware. Tried the upgrade utility that is comes with the firmware and it cannnot find the NMC, even if I specify the IP address. 
Next attempt:
I logged into the NMC via the console cable. Despite the documentation stating I need to connect on Speed 57600 mine connects on 9600.
I've looked at the Network management Card 2 Command line interface guide. Almost none of the commands are valid with my card.
But I did discover my firmwware:
firmware is 5.1.3
may 4th 2010
bootmon v.1.0.1
aug 3 2009
Really old!
Next step I've tried is to upgrade the firmware using Xmodem following steps on this page
https://www.apc.com/us/en/faqs/FA156047/
I cannot get the BM> menu it just goes straight to username request. I am hammering the enter key repeatedly.
 
Next step: buy a new card?
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • network
  • network_management_card
  • passphrase
  • PowerChute
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:37 AM

Hi,

Before upgrading be sure you are logging into the card as the root user. The default root user is apc with a password of apc. If you are not logging in as root you will not have access to the admin tab.

To reset the authentication phrase on the NMC select the UPS tab, go to shutdown, PoewrChute Shutdown Parameters. 

SMgIQyvB%2B1x9tYW8eIAz9g%3D%3D.pngSMgIQyvB%2B1x9tYW8eIAz9g%3D%3D.png

Have you tried to update the card using FTP? If you can FTP to the card you can upgrade. The FTP instruction are available in  FAQ FA156047. You should upload the Bootmon first, log out of the card, wait 60 seconds, log back in, upload the AOS, logout, wait 60 seconds, log back in upload the SUMX. 

To access Bootmon you need to connect at 57000. Connect the serial cable 940-0299, open the terminal program, set the com port, set the speed to 57000, using a paper clip press the reset button the the AP9630. Most cards you need to angle the paper clip up to press the top of the opening. The LEDs should start flashing and when they do begin to press the enter key.

Zt7M6An1LxvK5%2Fj0l0Ju3w%3D%3D.pngZt7M6An1LxvK5%2Fj0l0Ju3w%3D%3D.png

2a5aVQyHJfvVYzEZZyLDig%3D%3D.png2a5aVQyHJfvVYzEZZyLDig%3D%3D.png

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

SFSUMXxxx = Software Firmware SmartUPS-Matrix version number

SFSYxxx = Software Firmware Symmetra* version number *single phase Symmetra

You have a Smart-UPS so SFSUMX694 is the newest version:

https://schneider-electric.box.com/s/42v7xlug1pua1v9mkmbi7kstlpn6ko3l

Release Notes:

https://schneider-electric.box.com/s/25wvteu1ymx0wwr15uek5jjzeczt225a

-Gavan 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
6333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:04 AM . Last Modified: ‎2024-03-08 01:37 AM

Hi,

Before upgrading be sure you are logging into the card as the root user. The default root user is apc with a password of apc. If you are not logging in as root you will not have access to the admin tab.

To reset the authentication phrase on the NMC select the UPS tab, go to shutdown, PoewrChute Shutdown Parameters. 

SMgIQyvB%2B1x9tYW8eIAz9g%3D%3D.pngSMgIQyvB%2B1x9tYW8eIAz9g%3D%3D.png

Have you tried to update the card using FTP? If you can FTP to the card you can upgrade. The FTP instruction are available in  FAQ FA156047. You should upload the Bootmon first, log out of the card, wait 60 seconds, log back in, upload the AOS, logout, wait 60 seconds, log back in upload the SUMX. 

To access Bootmon you need to connect at 57000. Connect the serial cable 940-0299, open the terminal program, set the com port, set the speed to 57000, using a paper clip press the reset button the the AP9630. Most cards you need to angle the paper clip up to press the top of the opening. The LEDs should start flashing and when they do begin to press the enter key.

Zt7M6An1LxvK5%2Fj0l0Ju3w%3D%3D.pngZt7M6An1LxvK5%2Fj0l0Ju3w%3D%3D.png

2a5aVQyHJfvVYzEZZyLDig%3D%3D.png2a5aVQyHJfvVYzEZZyLDig%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

Hi Bill, 

Thank you for responding. 

You could be onto something there. i'm logging into the NMC as apc/apc but i'm wondering whether that username has been made into a user with another username being an actual admin. Originally it was installed by a third party.  Is there anyway of finding that out whether apc is not an administrator?

This is what i see when i log in as apc/apc

VZy7YrTONWHb3%2FT0Fjrcjw%3D%3D.pngVZy7YrTONWHb3%2FT0Fjrcjw%3D%3D.png

i think i'm connecting properly. i didn't get anywhere with putty so i've been using Tera Term. But yes, i stick the pin in (you can feel it engaging). Soon as I see the port light flashing green/red I start pressing enter. How long should I wait...after a few minutes I usually give up. Maybe i'll try Putty again.

I just tried the FTP method, that seemed to go further. But when i input the "Put" bin file i get 

command ok
error 550 STOR requested action not taken

so maybe apc/apc is not an admin

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

Hi Graham,

Have you tried to change the authentication phrase in the screen above and then matching it PCNS?

From personal experience the NMC can be a bit  funny with some FTP clients, I recommend using WinSCP:

https://winscp.net/eng/download.php

-Gavan

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

Hi Gavan, 

yes I had, several times in using all sorts of pass phrases. 

Thank you for all your help but I have managed to solve it. 

I have tracked down the person who installed the card originally back in 2010 and he had his notes on the install. As suspected the apc/apc user was changed to a user and he has given me the admin credentials. 

All this time I never thought to upgrade the card firmware and this issue only cropped up when i re-seated the card.

I have now logged on as an admin, changed the pass phrase and Powerchute can once again communicate with the card. Now i'm going to proceed with upgrading the firmware. 

Thank you to everyone for their assistance. 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Another Quick question before I go. 

I can see plenty of forum users who have sent the incorrect firmware for their NMC and it does say in the guides not to do that. 

I've gone to https://www.apc.com/shop/uk/en/products/UPS-Network-Management-Card-2/P-AP9630 to get the firmware and it lists two firmware files:

SFSUMX688
SFSY688

I cannot work out which one is correct for my NMC and UPS. The manuals for each file seem identical. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
6333
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

SFSUMXxxx = Software Firmware SmartUPS-Matrix version number

SFSYxxx = Software Firmware Symmetra* version number *single phase Symmetra

You have a Smart-UPS so SFSUMX694 is the newest version:

https://schneider-electric.box.com/s/42v7xlug1pua1v9mkmbi7kstlpn6ko3l

Release Notes:

https://schneider-electric.box.com/s/25wvteu1ymx0wwr15uek5jjzeczt225a

-Gavan 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Thanks Gavin, much appreciated. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
6332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Final Note: 

I tried FTP again. became stuck with
"150 File status okay; about to open data connection."

So I created a temporary firewall rule to allow port 21, 22 to go through then went back to the firmware update utility and changed to FTP method and off it went with no issues. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore