Configuring custom notification settings on many 9617s

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Configuring custom notification settings on many 9617s
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
4
1104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

Configuring custom notification settings on many 9617s

What can I do to set up one config that has all of our notification settings to multiple 9617s? Can I just use one config.ini?. I only want certain events within the event heirarchy (not every warning and not every critical) and doing this piecemeal will take forever and be prone to errors. Can I edit a single config.ini file and upload that or use that User Configuration File (ini) upload feature on the 9617? the config.ini file probably can't be bulk copied to each since it has the unique IP address, etc.
If I can't do anything easy, what part of the config.ini file can I just copy and paste into other config.ini files that is the Notification settings only?

thanks!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

I found the Readme that's included and have uploaded a config.ini to several units. One thing I've noticed is it overwrites the notification settings AND the device name. So when you get alerted, the IP is correct in the alert but the name itself is the same for everything now.
Another thing, I got several alerts from each device after they were upgraded saying "an external battery pack has been installed" and a few SNMP configuration change alerts, even though these are disabled in notifications. I was using version 1.0 of the utility, is there a newer version available anywhere?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
1104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

Hello,

The utility which you will want to use is the INIUtility. That will allow you to upload one config file to multiple devices, but only specific sections which are different on every card. That can be found when you unpack the firmware, or here:

ftp://ftp.apc.com/apc/public/hardware/nmcard/firmware/

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

0 Likes
0
1104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:37 AM

Thanks, thats great news. Are there some instructions for this utility?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1104
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Give me some time, I'll do a long look for it on Monday. It has to be in a manual somewhere.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

I found the Readme that's included and have uploaded a config.ini to several units. One thing I've noticed is it overwrites the notification settings AND the device name. So when you get alerted, the IP is correct in the alert but the name itself is the same for everything now.
Another thing, I got several alerts from each device after they were upgraded saying "an external battery pack has been installed" and a few SNMP configuration change alerts, even though these are disabled in notifications. I was using version 1.0 of the utility, is there a newer version available anywhere?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore