Adding PDU to Symmetra LX while unit is hot?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Adding PDU to Symmetra LX while unit is hot?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
3
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Adding PDU to Symmetra LX while unit is hot?

What is the risk of adding a PDU to a Symmetra LX with the unit powered on? I currently have a blank plate so I'd just be installing a new PDU, not removing an existing one.

I installed the current 2 PDU's when I first set up the unit and didn't have any problems at all hooking them up (the unit was de-energized). It seems like it would be easy to connect up the new PDU without connecting the wrong ends or them touching, or touching them.

I ask because taking my UPS all the way down to install the new PDU would be a big deal and if possible, I'd like to avoid it. I know that APC says that the unit must be unplugged and off, I just want to know if that is truly necessary.

Thank you!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Having swapped/installed some PDU's in our pair of LX's, I would say categorically that you are playing with fire if you attempt a hot PDU install. It is a bit of a wrestling match with the two or sometimes three molex connectors that provide the AC off the backplane - getting them plugged in, then tucking or jamming them into a very tight space and then screwing the PDU into place. You could accidentally touch one of the output receptacle contacts against the metal edge of the PDU opening and boom - you've got a short to ground - or your body.

Don't take the chance !
Dave

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

The risk is only having either 120, 208 or 240 VAC running through your body. Those wires are live, regardless if connected or not. APC will not be liable for any damage caused by installing a PDU Backplate into a Symmetra while the UPS remains on.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1206
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Having swapped/installed some PDU's in our pair of LX's, I would say categorically that you are playing with fire if you attempt a hot PDU install. It is a bit of a wrestling match with the two or sometimes three molex connectors that provide the AC off the backplane - getting them plugged in, then tucking or jamming them into a very tight space and then screwing the PDU into place. You could accidentally touch one of the output receptacle contacts against the metal edge of the PDU opening and boom - you've got a short to ground - or your body.

Don't take the chance !
Dave

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

0 Likes
0
1205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:05 AM . Last Modified: ‎2024-03-08 01:36 AM

Thanks for the feedback. Exactly what I wanted to know. I'll just need to figure out how to shut it off to install. Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore