PowerChute Network Shutdown

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
6
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

PowerChute Network Shutdown

Hi

Thanks to my previous question being answered (Thanks again) I have installed PCNS on a few servers and have created the script to shutdown exchange, which has been placed in the run this command file section on the configure shutdown page. It has been given 3 minutes to complete and the low battery duration has been set to 10 minutes.

Now I have a couple of questions about this set up, They are, do we need to do anything else or will the server get shutdown cleanly now that PCNS is installed and the command file has been set, or is there something that I have missed on the configure events page. This incidentally has confused me, I want this server to shutdown when the UPS has only 10 minutes of runtime remaining and for it to be shutdown cleanly. but don’t understand some of the options, battery discharge, does this option need setting to shut the system down when the ups is down to its last 10 minutes?

Sorry for the seemingly basic questions.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

hi,

dont be sorry for asking questions!

in PCNS, the configure events page can be configured to shutdown or run a command file based on several different types of events. (for example, if you wanted this particular server to shutdown after the UPS had run on battery after 1 minute to preserve battery power, you could do that on the configure events page.) by default, it will always shutdown though based on the low battery duration that you have set in the network management card. for configuration settings based on the low battery duration, this should be configured under Server name->Configure shutdown which states: When PowerChute shuts down your operating system, it will use these settings. Use the Configure Events page to select which events will cause the system to shut down.

so, if you have the low battery duration set to 10 minutes in the management card, the runtime should hit 10 minutes, and then your server with PCNS will receive this notification from the management card. then it will run the command file and after 3 minutes, proceed to do a graceful shutdown. (i also think and extra 2 minutes is thrown in the timeline here just incase anything unexpected happens, just for good measure and you cant disable that)

essentially, it sounds like you have configured everything correctly. if you want your server to turn back on after power is restored and the UPS reboots, then make sure you set your BIOS correctly. APC cannot assist you on doing that though. [you can refer to this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=948]

let me know if i missed anything or if you have any other questions.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1062
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

hi,

dont be sorry for asking questions!

in PCNS, the configure events page can be configured to shutdown or run a command file based on several different types of events. (for example, if you wanted this particular server to shutdown after the UPS had run on battery after 1 minute to preserve battery power, you could do that on the configure events page.) by default, it will always shutdown though based on the low battery duration that you have set in the network management card. for configuration settings based on the low battery duration, this should be configured under Server name->Configure shutdown which states: When PowerChute shuts down your operating system, it will use these settings. Use the Configure Events page to select which events will cause the system to shut down.

so, if you have the low battery duration set to 10 minutes in the management card, the runtime should hit 10 minutes, and then your server with PCNS will receive this notification from the management card. then it will run the command file and after 3 minutes, proceed to do a graceful shutdown. (i also think and extra 2 minutes is thrown in the timeline here just incase anything unexpected happens, just for good measure and you cant disable that)

essentially, it sounds like you have configured everything correctly. if you want your server to turn back on after power is restored and the UPS reboots, then make sure you set your BIOS correctly. APC cannot assist you on doing that though. [you can refer to this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=948]

let me know if i missed anything or if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

Thanks for the quick response.

So if i have got this right, the default installation is to shut the system down when the ups reaches 10 minutes remaining (or whatever time you set in the Management card, configuration, shutdown page. Plus the 2 minutes it adds here also) If you want this to change you have to configure events on the system (server) itself. Is this the Battery: discharge option or the Runtime: Exceeded ?

So with the configuration I have the server will run until there is 10 minutes of runtime left and then initiate the shutdown to the server which will run the ExchangeShutdown, wait 3 minutes and then shutdown?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

hi,

you are correct about what you mentioned on low battery duration.

if you want to shut something down at a different point other than the low battery duration, i would suggest configuring UPS:On battery event. so you could configure the UPS to shutdown (or even run a command file, notify a user) to happen after the UPS has been on battery for x amount of seconds.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

Great, thanks again for assisting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

Hi,

Having installed the network shutdown app on most of the servers and configured them idividually, is there any software out there that can manage the systems centrally, so I can group the systems and have different shutdown details for each group. It would be nice to be able to make one change and this be replicated out to all the systems, rather than having to visit each in turn.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

0 Likes
0
1061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:07 AM . Last Modified: ‎2024-03-08 03:13 AM

unfortunately, no. we dont have any tools for centralized management of powerchute software. it may be coming in the future though..

we only have tools for centralized management of network management cards and other networked accessories.

we do have a silent install procedure for deploying powerchute network shutdown to several machines but thats really for installing it. you'd have to reinstall it each time you want to make a configuration change and mass deploy it so i am sure you do not want to do that..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of