PowerChute Network Shutdown with more than 50 computers

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown with more than 50 computers
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All
Related Products
product field
Schneider Electric
Data Center and Facility 3 Phase UPS
product field
Schneider Electric
PowerChute Network Shutdown

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Luminarist
Luminarist
Cadet

Posted: ‎2022-03-17 03:54 AM

0 Likes
3
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-17 03:54 AM

PowerChute Network Shutdown with more than 50 computers

Setup: 

Redundant Galaxy VS UPS (2 units).

Workstations and servers totaling to more than 50 units.

 

I have tried to follow the application note (https://download.schneider-electric.com/files?p_enDocType=Application+solutions&p_File_Name=BKIR-6QW...) to apply on my setup but failing to get rebroadcast to work on unregistered units on the same segment.

 

Things that work.

Workstations/servers with PCNS installed and registered to the NMC work fine. They are shutting down as intended.

 

I am using silent install to get PCNS to install without NMC registration. Logs show TCP and UDP connections are established on the PCNS web UI. Have tried to configure "on battery" and "PCNS lose communication with NMC" events on 2 units registered computers and 1 unregistered computer on the same IP segment but the unregistered computer still won't shut down. Very confused on how to proceed, please advise.

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
  • Datacenter UPS
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-03-22 12:48 PM

0 Likes
2
1136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-22 12:48 PM

@Luminarist 

 

Does the shutdown fail for both events and have you run a packet capture on the system to see if it is getting the packets from the NMC? The NMC sends a UDP packet every 25 seconds and when switching to battery. If the PCNS client does not receive a packet for more then two minutes it will report lost communications with the NMC. When the PCNS client receives a UDP packet informing of a battery event it will react based on the configuration. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Luminarist
Luminarist
Cadet

Posted: ‎2022-03-22 06:14 PM

In response to BillP
0 Likes
1
1127
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-22 06:14 PM

@BillP As explained in original post, the configured event between NMC and registered PCNS client is working as intended. "On battery" and "PCNS lose communication with NMC" events are able to trigger the shutdown process. I am using "PCNS lose communication with NMC" event for convenience sake as it is easier to disable the port from the network switch to perform this functional test compared to breaker operation on the main distribution board.

 

The problem is on the NMC unregistered PCNS clients not behaving as intended. Referring to the application note, I am expecting to receive broadcast message from another NMC registered PCNS client on the same network segment to trigger the shutdown but it didn't happen.

 

So for example scenario on performing this functional test. 

UPS 1: 192.168.40.203

UPS 2: 192.168.40.204

 

Following application note, at least two PCNS shall be registered to NMC for reliability on rebroadcast.

NMC registered PCNS client A: 192.168.6.29 (Shutdown executed on configured event)

NMC registered PCNS client B: 192.168.6.30 (Shutdown executed on configured event)

 

Test subject

NMC unregistered PCNS client C: 192.168.6.31 (No shutdown triggered on configured event, even though PCNS configured to mirror the same shutdown event as clients A and B via silent install)

 

I will try to run packet capture next to gather information. But I think there is a lack of information from manual/application note on exact step by step needed for getting this NMC unregistered PCNS to work with NMC registered PCNS. For example, do I need to match the configured event on unregistered PCNS client with registered PCNS client? 

 

Side note, trying to prevent PCNS from registering with NMC as per last page of the application note will only put the PCNS client in a shutdown loop if "PCNS lose communication with NMC" event has been configured previously. However, if I perform silent install without NMC registration, then this event will not trigger. I think there is some unintended behavior here as well.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2022-03-23 08:12 AM

In response to Luminarist
0 Likes
0
1107
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-23 08:12 AM

@Luminarist 

 

I apologize for the misunderstanding. When I read " Have tried to configure "on battery" and "PCNS lose communication with NMC" events on 2 units registered computers and 1 unregistered computer on the same IP segment but the unregistered computer still won't shut down."

I was asking if the PCNS client that is not registered with the UPS shuts down when configured for an on battery event? And, when configured for shutdown due to lost comm? 

 

What I think you are now saying is, when configured of ran on battery event the UPS does not shutdown. When configured for lost comm it will shutdown but only if you edit the pcnsconfig.ini file and set enrolWithNMC = false? If that is the case when installing are you registering the PCNS client? And, if you run the silent install and set Register_With_NMC=no the PCNS client will not shutdown?

 

Other questions:

  1. What is the IP address and subnet mask of the NMC?
  2. What is the subnet mask of the PCNS clients?
  3. How many network segments are you configuring?
  4. May I see copies of the pcnsconfig.ini from one registered PCNS client and from the unregistered client? You can attach them to this post.
  5. Can the unregistered PCNS client ping the NMC? 

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of