PowerChute Network Shutdown for Synology NAS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute Network Shutdown for Synology NAS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
10
14301
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

PowerChute Network Shutdown for Synology NAS

Hello...  recently my company just purchased Synology NAS, and I think this device is great for putting UPS to sleep in case of power failure because the NAS is the last device to turn off, and it also draws very little power compared to other computer.

The problem is all of our Smart UPS are controlled by AP9619, and the Synology built in UPS function cannot turn off the UPS via UPS-SNMP mode.  Synology built in UPS function can turn off locally connected UPS (via USB port), but it is not viable in networked environment.

Could APC make PowerChute Network Shutdown for Synology DSM? 

I think Synology users are quite much coupled with the fact that APC is the most commonly used UPS brand, so I think that the effort to make PCNS for DSM won't be wasted.

Latest DSM version is 5.2

Thank you for your attention.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9619
  • apc
  • nas
  • network
  • NMC
  • PowerChute
  • shutdown
  • synology
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:38 PM

0 Likes
0
14293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:38 PM

On 4/16/2019 10:20 AM, Tommy said:

Run the installer: sudo /pathtoinstaller/install.sh

Examining the install.sh file, it appears the Java runtime is needed. Did you manually install this on the Synology unit? The one I am working on does not ship with it installed by default.

EDIT: I just noticed a jre tar file there, so I bet the installer actually unzips it locally.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

Hi,

I will send your request to the Product Manager. A network option you have now is to write a script PowerChute will run prior to OS shutdown that will command the Synology system down. Another option is to connect to the UPS via USB and use the built in shutdown option. You can have the Synology system connected to the UPS via USB while the other systems are communicating over the network.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

On 9/8/2015 4:48 PM, Bill said:

Hi,

I will send your request to the Product Manager. A network option you have now is to write a script PowerChute will run prior to OS shutdown that will command the Synology system down. Another option is to connect to the UPS via USB and use the built in shutdown option. You can have the Synology system connected to the UPS via USB while the other systems are communicating over the network.

Hi, 

Could you please advise if i can use Synology 916+ with APC BR1500 (BZ1500PBI-BR) model, via USB to shutdown? it will work with this model?

Thank you,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

Has there been any movement on this case? I have a synology nas and would also like to find a networked solution to this.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

On 5/11/2018 1:44 PM, Joel said:

Has there been any movement on this case? I have a synology nas and would also like to find a networked solution to this.

Hi,

i asked yesterday but didn´t have awnser yet, are you from Brazil too?

Im trying to find a network ups that can turn off synology NAS with a good price

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

You could try installing APCUPSd on your Synology NAS:

https://forum.synology.com/enu/viewtopic.php?f=27&t=19378

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

I would also be interested in this -  Bill would you be able to provide us with an update/status to this?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

Hi,

At this time, we do not offer PowerChute for Synology NAS. 

If the UPS is a Back-UPS or Smart-UPS you can connect the USB cable to the NAS and use the built-in shutdown interface to power down the NAS. 

If the UPS is a Smart-UPS and has an NMC installed you can install PowerChute Network Shutdown on a compatible system and write a command file / script to power down the NAS. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

I have installed PowerChute Network Shutdown 4.3.0 for linux on an RS2416+. It's working fine for me in combination with an AP9631 NMC card in the UPS. Seems to me your system should work too.

Here's what I did:

  1. Place the PCNS installer somewhere on the nas.
  2. Enabled SSH access.
  3. Access the NAS using SSH.
  4. Create a folder /etc/init.d
  5. Run the installer: sudo /pathtoinstaller/install.sh

Basically that's it. You probably need to configure the firewall.

Reply

Link copied. Please paste this link to share this article on your social media post.

tristan_apc
Crewman tristan_apc
Crewman

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:39 PM

After I ran sudo /pathtoinstaller/install.sh ssh returned:

Cannot find pcns430.tar.gz

Aborting with error code-15.

I can't think why as I can see pcns430.tar.gz in the folder alongside install.sh and there are no strange permissions on that directory that should mean ssh can see install.sh but not the pcns430 folder...

Please can someone help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:38 PM

0 Likes
0
14294
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:19 AM . Last Modified: ‎2024-02-29 10:38 PM

On 4/16/2019 10:20 AM, Tommy said:

Run the installer: sudo /pathtoinstaller/install.sh

Examining the install.sh file, it appears the Java runtime is needed. Did you manually install this on the Synology unit? The one I am working on does not ship with it installed by default.

EDIT: I just noticed a jre tar file there, so I bet the installer actually unzips it locally.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore