PowerChute Network Shutdonw
  • PowerChute Network Shutdonw
Posted: ‎2021-06-30 08:09 AM . Last Modified: ‎2024-03-07 03:29 AM
961
Hi guys
I install AP9619 in my UPS and PCNS to my two computer,. i set the PCNS to shutdown after power failure, Computer A set the time for 5 min. and the other one 20 min a Computer B. But when the power cutt-off then after 5 min. the two computer performed a shutdown, by rights the first to shutdown is the 5 min and the second PC after 20 min. but what happend is both PC shutdown after 5 min of power failure...
Any one can help me regarding this issue..thanks
Posted: ‎2021-06-30 08:09 AM . Last Modified: ‎2024-03-07 03:28 AM
yes the UPS turn off around 5 min after the shutdown of both PC shutdown and start-up gain because the power came back already.
Both computer was configure "Turn off the UPS after the shutdown finishes" and both computer was enable.
So only 1 PC must configure to enable the "Turn off the UPS after the shutdown finishes"?
Replies 4
Hi guys
yes it solve my issue.... thank you..its realy help me.
Thanks again
did the UPS turn off after both computers?
can you tell me, for each computer, whether or not under Configure Shutdown that the "+Turn off the UPS after the shutdown finishes (Not applicable to Parallel Silcon UPS and Smart-UPS VT).+" is selected (enabled) or not?
this should only be selected (enabled) on the SECOND computer to shutdown. it seems like possible you have it enabled on both, so when the first computer shutdown, it told the UPS to turn off which then in turn forced the other computer to shutdown.
let us know! thanks!