Power transfer detection

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power transfer detection
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
7
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

Power transfer detection

I have a Smart-UPS 2200 RM with AP9619 card / Hardware Revision: A10.

AOS Version: v3.6.1, sumx Version: v3.5.8

There is an automatic transfer switch that switches to natuaral gas generator during the power outage event.

APC detecs the power loss as it takes a min or two for the generator to kick in, but when the utility power comes back APCs don't detect the interuption as the switch back to the utility power is instant. Is there an SNMP value I can monitor that would indicate the return of the utility power?

 

Thanks

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • generator
  • power
  • snmp
  • switch
  • transfer
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

When the transfer switch switches back to utility power, if the switch happens "cleanly" enough (which depends on the transfer switch and any synchronization the generator does), the UPS just sees it as continuous "utility" power, regardless of whether it comes from the actual utility or your generator. Since it doesn't see a change, it won't alert you or change its SNMP status. You probably received an "On battery power" notification when the power failed and a "No longer on battery power" when the generator started, but nothing after that, right?

If the transfer switch is an APC model, it will report the switchover (and back). If it is a non-APC model, then you'd need to check with its manufacturer to see if it supports that type of notification.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
0
1560
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

When the transfer switch switches back to utility power, if the switch happens "cleanly" enough (which depends on the transfer switch and any synchronization the generator does), the UPS just sees it as continuous "utility" power, regardless of whether it comes from the actual utility or your generator. Since it doesn't see a change, it won't alert you or change its SNMP status. You probably received an "On battery power" notification when the power failed and a "No longer on battery power" when the generator started, but nothing after that, right?

If the transfer switch is an APC model, it will report the switchover (and back). If it is a non-APC model, then you'd need to check with its manufacturer to see if it supports that type of notification.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

Correct, I get "On Battery" alert and then a min later "No longer on Battery". No other alerts.

The transfer switch is ASCO, not an APC model. Even if ASCO supports the switch over notification I don't have any means to communicate with it and would require a communication module in the transfer switch to be installed.

I was hoping the switch over was not "clean" and APC could pick up the event, but it sounds like it can't.

Thanks for your help

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

I assume this is a big (whole building or at least datacenter-size) transfer switch?

Depening on what you want to accomplish by detecting that the utility power came back on, you might be able to get that from the generator management interface.

There are also various other things you can do that are rather oddball solutions if you really need the alerts and can't get them any other way. Post back if you want to hear about them.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:22 PM . Last Modified: ‎2024-03-04 10:46 PM

Only datacenter is on the generator, which is probably to my advantage. I have several PDUs in the building that are not on the generator. I can set up SNMP monitoring of their network interfaces.

When building looses power i will get a "communication lost" alert and when it comes back i should get a "communication established" alert.
Not sure if you had something similar to suggest, but would like to hear what you had in mind.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:46 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:46 PM

Three possibilities:

- Terry is correct and the switch transfers cleanly.

- The waveform distorts, but not enough for the UPS to pick it up. You can try adjusting the UPS' sensitivity to high, however then the generator's AC may not be clean enough.

- The UPS does detect the transfer, but the loss of power is too brief to be recorded by the network management card. If you have a microlink UPS lying around, like an SMT or SMX model, try plugging it in and seeing if it detects the transfer.

Overall, I think it's more robust to monitor the transfer switch or utility power directly rather than looking at the output of the switch.

Reply

Link copied. Please paste this link to share this article on your social media post.

wayne_i_apc
Lieutenant wayne_i_apc
Lieutenant

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

Have you considered using the input contact feature of your AP9619 card? If you connect a set of contacts on an external relay to the proper AP9619 terminals, then wire the relay coil to operate from UTILITY power only (NOT generator or UPS power), the NMC can be configured to send messages on a change of state of the relay indicating both the loss and restoration of utility power.

I'm not sure if this solution is something that Terry would consider "oddball", but it would require some hardware skill to (safely) assemble this relay solution from the basic parts, but there may also be a commercially available relay package.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

0 Likes
0
1559
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:23 PM . Last Modified: ‎2024-03-04 10:45 PM

It is kind of silly, but get an APC transfer switch and plug one source into the unprotected (before ATS) building power and the other source into the output of the UPS (this will likely need an adapter cable from 5-15P to L5-20R). Don't plug anything into the outlets on the transfer switch. Set the APC transfer switch to prefer the unprotected building power. Connect the network cable from the APC transfer switch to equipment which is also protected by a (possibly different) UPS, so that when it tries to send email / SNMP / whatever alerts, it succeeds.

When the utility power fails, the APC transfer switch will still be receiving power from the UPS it is plugged into. It will report a transition from source A to source B, via email / SNMP / whatever you configure. When the utility power comes back, the APC transfer switch will select that again (and send notifications) since you configured it to prefer that source.

Plugging one source of the APC transfer switch into the UPS is important, as otherwise it will lose power because your generator takes time to start after the utility power drops. While the management card in the APC transfer switch is booting, it can't send notifications. Having one of its sources plugged into the UPS guarantees that it will always have power and be able to report what is happening with the utility power.

As I said, kind of silly, but it does let you accomplish the monitoring you requested without getting involved in the building ATS / generator /etc. issues.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of