Runtime Minutes Don't Match Amps/Load

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Runtime Minutes Don't Match Amps/Load
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
2
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:17 PM . Last Modified: ‎2024-03-04 10:49 PM

Runtime Minutes Don't Match Amps/Load

Hi all, 

We're enterprise users of the Smart-UPS 3000RM (and some of it's slight and older variations), and these all have AP9630/31 or AP9617/18 NMCs. We have 142 centers, and each center has 2 of these in the rack, so we're reasonably familliar. We're now on our third UPS in about 6 months where the runtime remaining value is extremely low (2-3mins), and does not correspond to the amps/load (in the latest case today, 9.1amps and 2mins runtime). We've performed calibrations, self-checks, so-called manual calibrations (pull the UPS power cord and drain), and replaced the battery, and nothing seems to change this time value. We've also upgraded firmware to latest versions for the NMC. 

The three UPSs that this has happened to were slightly different models, and ages, but were all out of warranty (the one today, only by a few months). In the previous two cases we replaced the whole chassis (transferring over the battery and NMC from the old one without issue-- so it's likely neither of those components causing this), and this resolved. We don't believe in disabling or modifying critical notifications to work around, but we also take issue with spending thousands (including local vendor labor after prod hours) to replace a UPS chassis because of what we think may be a calculation or sensor bug. 

Has anyone run into this issue before? If so, does anyone have any solutions that worked, or at least some ideas to try? We're clearly not happy about only getting a little over 3 years out of a chassis, but we're hopeful this may be a known issue with some known solutions. 

Thanks to anyone for any input, 

Sean

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 3000
  • runtime
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:18 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:18 PM . Last Modified: ‎2024-03-04 10:49 PM

Hi Angela, 

Thanks for your response, and my apologies for not getting back sooner. For the latest example of this, the "About" in the nmc doesn't give me the SKU (below), and the unit is not onsite. I tried to loook up on the warranty lookup page, hoping I could narrow it down with the serial number, but it doens't work that way, apparently. Let me know if the information below isn't sufficient, and I will get someone onsite to get me the SKU from the physical unit. 

Model: Smart-UPS 3000 RM
Serial Number: AS1148142258
Firmware Revision: 666.6.D
Manufacture Date: 11/23/11

Also, I looked at a previous chassis that was replaced due to this issue (that we do have onsite), and it was a SUA3000RM2U (Serial # JS1032000066). Thanks for your offter to help, and please let me know if you need any more info.

Regards,

Sean

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:18 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
0
1032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:18 PM . Last Modified: ‎2024-03-04 10:49 PM

Hi Sean,

This may indeed just be a UPS firmware problem (not an NMC firmware problem) with a calibration not updating the runtime properly. To confirm that, I just need the specific model SKUs you're having a problem with i.e. SUA3000RM2U.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:18 PM . Last Modified: ‎2024-03-04 10:49 PM

0 Likes
0
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:18 PM . Last Modified: ‎2024-03-04 10:49 PM

Hi Angela, 

Thanks for your response, and my apologies for not getting back sooner. For the latest example of this, the "About" in the nmc doesn't give me the SKU (below), and the unit is not onsite. I tried to loook up on the warranty lookup page, hoping I could narrow it down with the serial number, but it doens't work that way, apparently. Let me know if the information below isn't sufficient, and I will get someone onsite to get me the SKU from the physical unit. 

Model: Smart-UPS 3000 RM
Serial Number: AS1148142258
Firmware Revision: 666.6.D
Manufacture Date: 11/23/11

Also, I looked at a previous chassis that was replaced due to this issue (that we do have onsite), and it was a SUA3000RM2U (Serial # JS1032000066). Thanks for your offter to help, and please let me know if you need any more info.

Regards,

Sean

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login